I don't fit EV charging points as I am not OLEV registered. However, I am fitting a Tesla EV charger soon for a friend as I owe him a favour.
The Tesla spec asks for a Type B RCD or Type A-EV RCD.
Looking at Regulation 722.531.2.101 this sates the same as above.
The regulation states a Type A RCD AND appropriate equipment that provides disconnection of the supply in the case of DC fault current above 6mA.
Is this 'equipment' located in specific Type A RCD, or in certain EVCP's, or a seperate piece of equipment?
The tesla wall charger spec says it does not measure DC current leaking.
It sounds easier just to go for a type B RCD but it is difficult to locate one, could any EVCP installers send a link?
Thanks