Discuss Why ? 120-130v old tester in the UK Electrical Forum area at ElectriciansForums.net

Dustydazzler

-
Esteemed
Arms
Supporter
Reaction score
8,197
So, I was messing around yesterday with some old testers I have laying around to see if they still work

I found my dads old Robin MFT and noticed something I have never noticed before

When you test of the EFLI setting put live and neutral probes on a switch or socket but don't connect the earth probe you get 120-130 ish volts.
Soon as you clamp the earth lead on it jumps back to 230-240V

Why is this ?
 
I assumed some sort of fail safe. Its a 3 lead tester and if you don't connect the earth lead to either the CPC or onto the N you get the red warning light which I knew happened but never ever noticed a voltage reading of around 120-130v.
 
I tried an old Robin 3-wire fault loop tester

Leaving off the earth shows 0 on the LCD display

P-N neon indicator is fully lit

N-P neon reverse indicator is partially lit
 
I tried an old Robin 3-wire fault loop tester

Leaving off the earth shows 0 on the LCD display

P-N neon indicator is fully lit

N-P neon reverse indicator is partially lit
The old Robin MFT I have if you put the red probe on live and black probe on teh neutral you get 120-130V showing on the display but the RED warning light is on and if you press the test button nothing happens. When you put the green lead and clamp it on the CPC it jumps to 240v and the green light come on and you can procede with test
 
The dear old Robin and Kyoritsu testers (and early Kewtech) do the high current loop by comparing "loaded" mains with unloaded mains.
A 10 ohm load is added between Line and Earth for a couple of +ve cycles. This charges up a certain capacitor.
Neutral to Earth (i.e. unloaded mains) then charges up a different capacitor for a couple of +ve cycles.
(There's also a wave rectifier making sure the charging happens very briefly and only during a couple of positive cycles to avoid overheating the relays or the load resistors)
Then the two capacitor voltages are compared and the loop impendence is estimated using the calibration constants.

They therefore need a 3 wire supply, and that's why you see the 120v if one of the returns isn't there.
This method was still used as late as the Kewtech KT63, the earth and neutral leads are externally joined to do a 2 wire loop test.

(Megger instead use a relay to switch in and out the test load and can use the same 'return' for both measurements, so their 2 wire hi-current doesn't need a Neutral)
 
The dear old Robin and Kyoritsu testers (and early Kewtech) do the high current loop by comparing "loaded" mains with unloaded mains.
A 10 ohm load is added between Line and Earth for a couple of +ve cycles. This charges up a certain capacitor.
Neutral to Earth (i.e. unloaded mains) then charges up a different capacitor for a couple of +ve cycles.
(There's also a wave rectifier making sure the charging happens very briefly and only during a couple of positive cycles to avoid overheating the relays or the load resistors)
Then the two capacitor voltages are compared and the loop impendence is estimated using the calibration constants.

They therefore need a 3 wire supply, and that's why you see the 120v if one of the returns isn't there.
This method was still used as late as the Kewtech KT63, the earth and neutral leads are externally joined to do a 2 wire loop test.

(Megger instead use a relay to switch in and out the test load and can use the same 'return' for both measurements, so their 2 wire hi-current doesn't need a Neutral)
How do you know all this ?:mask:
 
Screenshot_20240308_093908_Chrome.jpg
 
How do you know all this ?:mask:
I have a dangerous fascination for wanting to know how things work. In this case I got hold of some service manuals which for this age of gear are generally well written documents.
One of the reasons I still use a 1553 tester is that I have the 15 series service manual. I've been trying to get hold of a 17 series service manual for years now!
 

Reply to Why ? 120-130v old tester in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
826
We are currently renovating an old house after recently moving in. Whilst purchasing the property we received written assurances that the original...
Replies
47
Views
5K
Well I picked up a couple of non working Nova pat testers they both fail at the bot stage one just gives a line of boxes and the other halts at...
Replies
0
Views
601
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I have just popped out to a frustrated customer who has had intermittent tripping of a 30mA RCD for years, on average 5 - 10 x p/month. It used to...
Replies
31
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock