Discuss Why can't you join 6mm and 2.5mm? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
70
Saw this thread in the DIY forum but can't respond and i have a question:

We are getting our bathroom refurbished , our bathroom already had a 9.5kw shower we are getting that changed to a rainfall shower.
As we have low water pressure we are having a water pump installed.

The builder has connected the existing 6mm cable to 2.5mm cable (using a connector block ) for the socket for the water pump.

Is this safe ?
Everyone seems to be going mad in the thread suggesting it's dangerous but this seems fine to me.

Since it's only a pump now, as long as the MCB is downrated to a max of 20a it should be fine, no?

Sorry if it's a stupid question but i'm a trainee and just getting to grips with all the science.
 
The reason it was considered dangerous was because our multi-talented builder jointed it by way of unenclosed block connectors. This is the thread in question.
 
Yes, as Westy says.
That particular thread, the builder had reduced the csa of the cable, but hadn’t downgraded the mcb to suit.
It is explained throughout the thread that reducing it to a 20A supply would solve the issue.
 
20A!! what size pump is being used? A 6A mcb would probably be more than adequate for a shower pump.
The cable joint needs to be within a propriety enclosure, and maintenance free if inaccessible.
 

Reply to Why can't you join 6mm and 2.5mm? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
We are getting our bathroom refurbished , our bathroom already had a 9.5kw shower we are getting that changed to a rainfall shower. As we have...
Replies
12
Views
3K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K
I have a submersed bore pump 85M down and covered by 40M water. The motor/pump is 1.1HP, capacitor run, 35uF in a capacitor box above ground, with...
Replies
5
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock