- Reaction score
- 5,628
I'm reading a thread at the moment about a 9.8kW shower that has been installed on a 6mm cable. My natural instinct was to think that's wrong, it should be on a 10mm. Most of us would fit a 10mm cable and believe that to be to the right choice but if the reference method is C then the 6mm has a CCC of 47A and is fine isn't it? I suppose you could argue that you should fit a 50A breaker but we all know a 40A breaker will be absolutely fine. You would have to have a constant shower for perhaps a year for a 40A MCB to trip with 42.6A running through it. In fact I doubt it would even trip then.
We don't seem to question a similar scenario, i.e a 4mm radial on a 32A MCB where virtually all reference methods bar C (in a domestic situation) give a CCC <32A.
We don't seem to question a similar scenario, i.e a 4mm radial on a 32A MCB where virtually all reference methods bar C (in a domestic situation) give a CCC <32A.