Discuss Why is oven tripping rcd? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
36
Every time oven gets to temperature it trips the RCD. Thought the oven must be knackered so got a new one. That does the exact same thing. Any ideas? I should add that this is a brand new house. Just moved in yesterday
 
I would get an electrician to test the supply cable to the oven, being a new house does not mean much as it could be a nicked or pinched cable at an accessory & underload trips. Get an electrician to test the complete circuit including the Earth integrity at the oven, and look for excessive earth leakage as well.
 
My oven is very temperamental , it trips the rcd sometimes when I turn it on and sometimes when I turn the main dial off

I have done all the tests on the cable between the consumer unit and the cooker connection plate and it all test fine
 
My oven is very temperamental , it trips the rcd sometimes when I turn it on and sometimes when I turn the main dial off

I have done all the tests on the cable between the consumer unit and the cooker connection plate and it all test fine

Get Delroy round 😀 He's got an MFT now I believe
 
If it happens every time and you have changed the oven then it is very unlikely to be the oven, more likely a wiring fault.

Simple faults typically would trip instantly so the suggestion above that it is something getting hot and triggering it makes sense.

My own oven (30 year old NEF thing) trips the RCBO around twice a year, typically though when I turn it off so probably just neutral breaking first or similar causing a little current spike. Usual static checks (IR and leakage current) did not show anything to worry about, just a mild annoyance due to the fscking stupid location of my CU. But one I could not realistically change when replacing it a couple of years back.
 
Get Delroy round 😀 He's got an MFT now I believe
Indeed He has a lovely shiny Megger

But I don't see how is Megger would show anything different than my old Fluke does

I have IR the cable , done an EFLI test and RCD test and all the tests are fine

That said I would love an excuse to meet Del and the banter would be worth the £150 call out fee , even if he didn't manage to fix me oven
 
Just thinking about my case - I wonder if the OP's oven has been wired reverse polarity to the thermostat is breaking the neutral?
Definately worth checking.The common factor is that both ovans tripped rcd when desired temperature is reached.It would seem the temperature itself is not the trigger but the circuit that is been switched as a result of the temperature.The switching mechanism may well be the key to the probem and checking polarity would be a good place to start
 
How many times has the new oven tripped the RCD? The type of element typically used for ovens can absorb moisture if left unused from new for a while in less than perfect conditions, and from the time when I used to repair the odd domestic appliance, I know that it's not at all unusual for a new element of this construction (oven, grill, or old type spiral hob) to electrically leak enough to trip a RCD as it heats up. Typically, the leakage resistance will be satisfactory when the element is cold, and decrease as it heats up.
After a while, the moisture is driven out, and the element stays within leakage limits.
 
Brand new house the OP moved into yesterday!

Was the oven new? If not, and it hadn't previously caused issues (assuming it was powered by an RCD protected circuit), had it been in storage for a period of time? Was the replacement oven new?

It seems odd to buy a new oven to replace one that is a day old.
 

Reply to Why is oven tripping rcd? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I have just replaced my old double oven which was about 10 years old with a new model as whenever I used the top oven it tripped the electrics...
Replies
1
Views
631
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
849

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock