Discuss Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

No spark worth his salt is fitting split load boards these days IMO.

RCBO & SP is all I quote for.
 
I know that but OSG is supposed to be a bite-sized, easy reference for whats in the big brown book. Seems like the OSG talks a lot of gibberish.

Here's another one.

OSG page 61.

'Other than at the origin of the installation, every circuit...that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.'

This basically says all breakers have to be double pole in a TT, no?

Yet you go to 132.15.201 which the OSG references and it says absolutely nothing about this.
The DP main switch makes it compliant.
 
But that reg says supply side of the incoming device eg main switch. **** me these books are confusing. Someone should rewrite them in normal language, they'd make millions.
It does also mention the internal wiring I think. Says something about them being double insulated or
reinforced.
 
Only as it pertains to a pre-assembled board's link cables as far as i can see.
'Regulation 531.3.5.3.2.201 requires that where Class I enclosures are installed in installations forming part of a TT system and RCD protection is used on outgoing circuits, all live conductors on the supply side of the incoming device must have double or reinforced insulation'.

Taken from NICEIC website.
 
That quote though says that all individual circuits must have their own DP isolating device. Yet the regs don't mention it.

It does mention 'without interrupting the supply to other circuits'.
I'm sure it says somewhere “that provision may be made for isolation of a group of circuits by a common means”
 
531.3.2 (ii)
It does say 'considered'.
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.
'Regulation 531.3.5.3.2.201 requires that where Class I enclosures are installed in installations forming part of a TT system and RCD protection is used on outgoing circuits, all live conductors on the supply side of the incoming device must have double or reinforced insulation'.

Taken from NICEIC website.
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.

NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.

From the book.

Supply side of eg main switch is massively ambiguous imo.
 
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.

For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.

NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.

From the book.

Supply side of eg main switch is massively ambiguous imo.
You were asking about the main tails and argued that :-
Only as it pertains to a pre-assembled board's link cables as far as i can see.
I was merely pointing out that it does mention DI tails or reinforced insulation.
 
That quote though says that all individual circuits must have their own DP isolating device. Yet the regs don't mention it.

If that were the case would it mean that all the 1000s of consumer units that use mcbs are not compliant ?
 
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.

For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.

NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.

From the book.

Supply side of eg main switch is massively ambiguous imo.
It doesn't say required it suggests them.
 

Reply to Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
914

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock