Discuss Why neutral and hot reversed only when a/c is turned on? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I have tenants that have 3 fairly new small a/c units all the same and when any of them are turned on my tester reads hot & neutral reversed. The 15 amp circuit that feeds these units has no ground wire. Is this normal or could these a/c units be wired wrong from the factory?
 
The 15 amp circuit that feeds these units has no ground wire. Is this normal or could these a/c units be wired wrong from the factory?
Do you mean the circuit in the house has no ground? I would be surprised if that is allowed in the USA!?

I would be more ccncernd there is something wrong with the house wiring, maybe a high resistance neutral or similar, and suggest you get a professional electrician to check it more thoroughly than a socket tested does.
 
Do you mean the circuit in the house has no ground? I would be surprised if that is allowed in the USA!?

I would be more concerned there is something wrong with the house wiring, maybe a high resistance neutral or similar, and suggest you get a professional electrician to check it more thoroughly than a socket tested does.
It is not allowed in the US I juust found out when I rehabed the apartment .The wiring was updated about 12 years ago for these 3 rooms so all of the new wiring has a ground other than the line that comes from a junction box and I am going to be running a new line with a ground in a couple days. It was the reversed hot & neutral that I wasn"t sure about. Why is this happening?
 
if the circuit they are connected to has no ground connection, it may well be against reg's.
@Megawatt will be better to advise on that.

however, if there is no ground reference, your tester is unlikely to be able to be able to accurate information about hot and neutral being reversed as it uses the ground to reference the voltages against.
 
I have tenants that have 3 fairly new small a/c units all the same and when any of them are turned on my tester reads hot & neutral reversed. The 15 amp circuit that feeds these units has no ground wire. Is this normal or could these a/c units be wired wrong from the factory?
Gasoline all you need to do is take the receptacle out and the black wire goes on the gold screw and the white goes on the silver screw. That’s where your polarity is crossed
[automerge]1593282303[/automerge]
I have tenants that have 3 fairly new small a/c units all the same and when any of them are turned on my tester reads hot & neutral reversed. The 15 amp circuit that feeds these units has no ground wire. Is this normal or could these a/c units be wired wrong from the factory?
As far as the absence of a ground yes a lot of old houses don’t have grounds from many years ago and as far as code enforcement goes if you replace the receptacle or light or anything you have to install a ground wire from the panel. Anything you work on you have to bring it up to code.
[automerge]1593282547[/automerge]
I have tenants that have 3 fairly new small a/c units all the same and when any of them are turned on my tester reads hot & neutral reversed. The 15 amp circuit that feeds these units has no ground wire. Is this normal or could these a/c units be wired wrong from the factory?
I worked on a house yesterday that had no ground and it was the old cloth insulation wire. I had to go up in the attic and replace the old wiring to bring it up to today’s standards.
 
Last edited:
It is not allowed in the US I juust found out when I rehabed the apartment .The wiring was updated about 12 years ago for these 3 rooms so all of the new wiring has a ground other than the line that comes from a junction box and I am going to be running a new line with a ground in a couple days. It was the reversed hot & neutral that I wasn"t sure about. Why is this happening?

How are you testing this apparent polarity reversal?

I don't see how you can test polarity without a ground to use as a third point of reference.

If you measure between hot and neutral you will see 120V (if I understand USA terminology and voltages correctly) if you swap the leads of the tester you will measure exactly the same voltage. AC doesn't have an easily established polarity the same way DC does, it is only when you bring a third point of reference into the measurements, such as a ground, that you can establish a polarity.
Once you have a ground you can measure between hot and ground, then neutral and ground to establish which one is at ground potential and which one is at 120V to ground.

If it is a tester, such as a socket tester, which connects to hot, neutral and ground then gives simple results such as OK, polarity reverse, missing neutral etc then being totally without a ground it will lijely be confused and behave erratically.
[automerge]1593282972[/automerge]
Gasoline all you need to do is take the receptacle out and the black wire goes on the gold screw and the white goes on the silver screw. That’s where your polarity is crossed

We don't know for sure that the polarity is wrong, we only know that there is no ground and an unknown type of tester has indicated a wrong polarity. This could easily be the tester being unable to function correctly without a ground and giving a false reading.
 
Gasoline all you need to do is take the receptacle out and the black wire goes on the gold screw and the white goes on the silver screw. That’s where your polarity is crossed
[automerge]1593282303[/automerge]

As far as the absence of a ground yes a lot of old houses don’t have grounds from many years ago and as far as code enforcement goes if you replace the receptacle or light or anything you have to install a ground wire from the panel. Anything you work on you have to bring it up to code.
[automerge]1593282547[/automerge]

I worked on a house yesterday that had no ground and it was the old cloth insulation wire. I had to go up in the attic and replace the old wiring to bring it up to today’s standards.


I checked all receptacles on that circuit and they are all wired correctly black wire to gold screw and white to silver screw and hot is black wire. Like I stated in first post the tester reads fine other than no ground (which I will be running a new 14awg wire so that issue will be corrected) but the hot and neutral reversed is what I was concerned about it only reads on tester if the a/c units are running
[automerge]1593283542[/automerge]
Sorry I did not know if the no ground issue was the cause of the problem. \
and this is the tester that I am using
 

Attachments

  • electrical tester IMG_20200627_143824059.jpg
    69.1 KB · Views: 15
Last edited:
As above, the lack of a ground wire in the circuit is confusing the tester. It might indicate OK with the A/C's switched off, but when you switch them on, the normal small amount of ground leakage coming back down the cord to the outlets that has nowhere to go, makes the ground prong partially hot. The tester sees too high a voltage between what is supposed to be ground and neutral, and too low between ground and hot, and interprets this as a reversal of hot and neutral.
 

Reply to Why neutral and hot reversed only when a/c is turned on? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

have a GFI outlet. I have not shut tge electricity off to the wires, they were live. I have the white neutral wire hooked up to the outlet. I have...
Replies
4
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
TLDR: In a 3 wire service are the ground and the neutral always bonded, in all subpanels? House made in 1970 has the meter and a 150 amps breaker...
Replies
3
Views
2K
Hi - I'm trying to add an additional outlet to a circuit in my house. I tested the outlet with a tester, and it showed as correct. The existing...
Replies
1
Views
960

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock