Just finished installing 20 x spike lights in a customers front garden. 2.5mm SWA ran from existing junction box feeding existing fence lights. All pulling no where near 1A in total.

When all connected and wiring tested, went to switch on MCB and it popped. Rendering the MCB useless as if L-N fault. Spend an hour going round checking every single connection and also to make sure no cuts in armour cores etc. All fine. Changed MCB and reset. Straight away it popped again.

I then disconnected all of the spike light load cables Line and Neutral. Reset MCB and all fine. The existing fence lights worked no issue. Connected in 1 spike light and reset MCB. Popped again. So I assumed this was a faulty unit, however it did this with another 3 before I stopped And began to pull my hair out.

I then got an LED floodlight and flexed it up, connecting it into the same connections as the spike light had been in, and it worked absolutely fine.

The customer then asked me to fit a plug top to a new spike light, which was the same but never fitted as it was extra , I did and when switched on it popped the MCB and rendered the socket outlet useless.

The spike lights are 7W LEDs with a black 2core flex brown and blue cabling. I even tried reverse polarity on them and still the same issue.

I pretty much put it down to faulty lights, but the fact there is 20 of them is making me second guess myself. Anyone here have any experience with this ? I have 16 years experience and never heard anything like it.

Any help appreciated.

Nick
NEB Electrical Ltd
 
Guys

They are all 24v !!!! I just had a look at the tiny label .. I went off the box they came in which had mains power on it and the fact they were supplied with no driver etc (customer supplied)

Actually kicking myself. Been such a long day today. I actually cannot believe I overlooked that. Oh well looks like they are for the bin then and an expensive job for me.

Thanks again

Nick
 
Guys

They are all 24v !!!! I just had a look at the tiny label .. I went off the box they came in which had mains power on it and the fact they were supplied with no driver etc (customer supplied)

Actually kicking myself. Been such a long day today. I actually cannot believe I overlooked that. Oh well looks like they are for the bin then and an expensive job for me.

Thanks again

Nick

These things happen. At least you found it.
 
Guys

They are all 24v !!!! I just had a look at the tiny label .. I went off the box they came in which had mains power on it and the fact they were supplied with no driver etc (customer supplied)

Actually kicking myself. Been such a long day today. I actually cannot believe I overlooked that. Oh well looks like they are for the bin then and an expensive job for me.

Thanks again

Nick
Fair play to you @NEB Electrical nick for putting ya hands up ?
 
Lack of cpc gave the game away!! Sickening!! Reckon u better open a beer and try and forget the whole affair!!
[automerge]1569963582[/automerge]
Who's brave enough to own up to some "I could kick myself" moments?
Running in black 3core flex instead of co-ax, and not realising till 2nd fix was pretty embarrassing..
 
Last edited:
Aw man I feel for you. Mistakes happen though. I've wired an entire house lighting in twin brown rather than T&E before (wholesalers sent me the wrong cable and I never noticed till 2nd fix). Another job 1.5mm Hi Tuff instead of Co Ax (Shocker really, other than being black in colour they are nothing like the same)
 

Reply to Why would spike lights trip an MCB as if a dead short is present ? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
448
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I have a Security Light on my patio and until recently it worked fine. It stopped working and I couldn't decide if it was the LED Floodlight or...
Replies
6
Views
507
Hey guys, looking for a bit of advise on the installation of an outside light. I plan on chasing out the plasterboard and running a cable from a...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock