Discuss Wind Calculations in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

M

MCS Renewables

Hi
Had our two day MCS audit this week. Three technologies produced two non conformances .

Solar PV and solar thermal ...no wind load calculations.

Having read the entire section on wind calculations I am still at a loss as to how to do the calculation and what to do with the figure when arrived at. ( Not to mention why ?! )

Any help or ideas or samples would be appreciated

Thanks
 
We had our structural engineer build a virtual property in his software (TEDDS) that was worse than the worst scenario we come across. We have uplift figures for all roof sectors.

The mounting system we use has been tested by BRE, so we have the failure and typical figures for each bracket.

Dividing one into the other gives us figures for configuration of mounting system.

Assessor well impressed on surveillance visit.

Dead load is unlikely to be an issue. Calc is easy.

Just watch old roofs or unusual structure/construction. That is when you need to consult your structural engineer.
 
It was working last night.

EDIT: I've just noticed my link is different to worcester's http://easy-pv.co.uk/index.php

All the other calculations seem to work for me but not the Windload calculations. I just put 1000 brackets in and still not enough. Maybe me somthing I am doing?

Even at 2kg/fixing it gives me a fail.

Capture.JPG
 
Thank you for checking, thought it might :)

I have even tried it on a different computer. Do you mind showing me what you input? Do you have to work through all of the roof calcs or can you skip to the Windload calc on it's own. We have touch screens that allow you to skip through to windload by swiping.
 
Sorry for Slow reply, just done our local Fireworks. All very strange I have tried different computers and different browsers. It seems to calculate the total windload correctly it just seems to calculate the pullout force calculation it seems to throw up the anomaly. I can't see where it is going wrong.

Capture 1.JPG

Capture 2.JPG
 
Sorry for Slow reply, just done our local Fireworks. All very strange I have tried different computers and different browsers. It seems to calculate the total windload correctly it just seems to calculate the pullout force calculation it seems to throw up the anomaly. I can't see where it is going wrong.

View attachment 21289

View attachment 21290

For some reason it seems to be only putting 1mm as the screw penetration, despite putting 80mm in the dropdown box.
 

Reply to Wind Calculations in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
779
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
737
Hello, hopefully ive got this right but if someone can check over my maths for me, id appreciate it. Im needing to install a new supply cable...
Replies
3
Views
890
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock