Iv wired in lots of regular Y & S plan heating systems with the regular one pump. However this job i’m going to tomorrow (not seen it yet) has 4 Heating Zones and 1 Hot water Zone, the plumber said i need to ensure when one zone runs it doesn’t back feed and cause another zones pump to run, he said i probably need relays.

Normally the pump is wired onto the orange of the diverter valve along with the boiler switch wire, however i thought if i wired each zones pump onto the corresponding zones Brown wire of the diverter valve there’s no way one zone could power another zones pump.

Is there anything wrong with doing this? I can’t see any reason why this would be a problem and it means i don’t need relays.

(plumber says the boiler is capable of running all zones at once)
 
TL;DR
Can i wire each zones Pump onto its corresponding valves ‘Brown’ wire instead of fitting relays? to stop back feeding.
Only issue I can think of is that the pump will be pushing on the valve for a few seconds until it opens up fully.
 
I've done this before and there were no issues, the valve opens up pretty quickly so I don't think it'll do the respective pump any harm.
 
If you are using the brown of that zone valve what controls that valve.
Usually it’s the room stat.
Will you be using the orange & grey in that situation
 
Heating pump is centrifugal, so takes LESS power pumping into a closed pipe than an open one, also, there should be some kind of pressure operated bypass valve between pump and valve, so that argument isn't relevant anyway.
Pump from the brown is the way to go. Don't take electrical advice from plumbers.
 
If you are using the brown of that zone valve what controls that valve.
Usually it’s the room stat.
Will you be using the orange & grey in that situation
Got where your coming from now…Stat controls valve & pump, use the valve switch connected to the orange & grey for boiler signals Ls Lr…
 
Iv wired in lots of regular Y & S plan heating systems with the regular one pump. However this job i’m going to tomorrow (not seen it yet) has 4 Heating Zones and 1 Hot water Zone, the plumber said i need to ensure when one zone runs it doesn’t back feed and cause another zones pump to run, he said i probably need relays.

Normally the pump is wired onto the orange of the diverter valve along with the boiler switch wire, however i thought if i wired each zones pump onto the corresponding zones Brown wire of the diverter valve there’s no way one zone could power another zones pump.

Is there anything wrong with doing this? I can’t see any reason why this would be a problem and it means i don’t need relays.

(plumber says the boiler is capable of running all zones at once)
How did you overcome this? I’ve been exact same scenario, 4 valves, 2 pumps, pump shares 2 valves. Plumber says pump on and only one valve. How do you split the valves so they don’t open together on the brown?
 
Iv wired in lots of regular Y & S plan heating systems with the regular one pump. However this job i’m going to tomorrow (not seen it yet) has 4 Heating Zones and 1 Hot water Zone, the plumber said i need to ensure when one zone runs it doesn’t back feed and cause another zones pump to run, he said i probably need relays.

Normally the pump is wired onto the orange of the diverter valve along with the boiler switch wire, however i thought if i wired each zones pump onto the corresponding zones Brown wire of the diverter valve there’s no way one zone could power another zones pump.

Is there anything wrong with doing this? I can’t see any reason why this would be a problem and it means i don’t need relays.

(plumber says the boiler is capable of running all zones at once)
How did you overcome this? Have exact same scenario but can’t figure how to have zone valves not open with the other and have pump independent? He mentioned relays but I’ve never wired a relay so can’t figure how it’ll work.
 

Reply to Wire Pump to Diverter Valve ‘Brown’ or use a relay? in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
937
For the past few years, I have used a hydronic system (outdoor wood boiler) with both high and low temp working simultaneously. The low temp...
Replies
6
Views
762
Hi there, the heating system I am working on has 6 zones and valves for each zone which was working fine with one boiler and one pump. some rads...
Replies
1
Views
1K
Friend asked me to wire in a hive on a conventional 1 zone heating system. So I fitted it tested the HIVE and all was working. I then said to him...
Replies
5
Views
863
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock