Discuss Wiring a 4-Function, 3-Switch Wall Control in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
7
Before you write go get an electrician - I HAVE! And he's never wired one before. AND asked ME to do some research!! Before you also say get a new one - though boy do I want one - it is a long story and not an option.


The switch is to control a bathroom vent fan with an inbuilt light, nightlight and heater - hence the 4 functions. Two switches are normal on-off for the fan and heater, whilst the third has a rocker position to accommodate the light, nightlight and off. Love this switch option which controls all the functions whilst only using 1 gang, so separating it into 4 different switches is something I won't consider (he suggested this option).


The wiring diagram shows three loads going into the junction box, but the electrician has 4 wires for each function coming out of the vent unit. Perhaps the two light functions need to be spliced inside the junction box before connecting to the switch? He doesn't seem to know how or where to integrate the 4th function.


Anyone have any insights? They would be MOST appreciated so I can get back to picking out my sconces :)


Fan:
View: https://www.amazon.com/Broan-Nutone-9093WH-Exhaust-Bathroom-1500-Watts/dp/B001PO29TA/ref=pd_sbs_60_t_0/140-7652250-2779335?_encoding=UTF8&pd_rd_i=B001PO29TA&pd_rd_r=c8ccce8a-7fe9-46af-9271-6daa0eefe2b2&pd_rd_w=DY487&pd_rd_wg=jIsMb&pf_rd_p=5cfcfe89-300f-47d2-b1ad-a4e27203a02a&pf_rd_r=03X2D3K22GHVYNS127ZK&psc=1&refRID=03X2D3K22GHVYNS127ZK



Switch:
Bath and Ventilation Fans Range Hoods Fresh Air Systems - Broan - https://www.broan.com/Accessories/Bath-Ventilation-Accessories/List-of-All-Accessories/77DW


Installation guide:
broan.com/BroanPublicWebSite/media/BroanUS_Canada/Documents/installation_guides/77DV-77DW-Installation-Guide-99043742B.pdf?ext=.pdf
 

Attachments

  • thumbnail_IMG_9631.jpg
    76.1 KB · Views: 8
  • thumbnail_IMG_9629.jpg
    107.5 KB · Views: 8
  • thumbnail_IMG_9628.jpg
    89.8 KB · Views: 8
  • thumbnail_IMG_9627.jpg
    76.5 KB · Views: 7
  • thumbnail_IMG_9626.jpg
    133.6 KB · Views: 8
  • thumbnail_IMG_9625.jpg
    62.1 KB · Views: 9
  • thumbnail_IMG_9624.jpg
    134.5 KB · Views: 8
This is how it looks to me:

The switch has two sections: Two ordinary switches sharing a common hot feed (connected with the screw terminals) and a completely independent 3-position switch with its own hot feed (connected by the captive wires). The ceiling unit simply has four hot inputs, neutral and ground.

At the switch, as shown in the instructions, the hot feed needs to split to the common side-wire terminal (to feed the two regular on/off switches) and to the captive black wire (to feed the 3-position switch). Then the four functions of the ceiling unit are connected to the four switch outputs.

Night light (black) to 3-position switch red (one 'on' position)
Main light (yellow) to 3-position switch blue (other 'on' position)
Heat (red) to one on/off switch screw terminal
Fan (blue) to the other on/off switch screw terminal.

It's not shown which of the 3-position switch red and blue outputs corresponds to which switch rocker direction. You might want to swap those over to get the switch operating in the direction you want.
 
This is how it looks to me:

The switch has two sections: Two ordinary switches sharing a common hot feed (connected with the screw terminals) and a completely independent 3-position switch with its own hot feed (connected by the captive wires). The ceiling unit simply has four hot inputs, neutral and ground.

At the switch, as shown in the instructions, the hot feed needs to split to the common side-wire terminal (to feed the two regular on/off switches) and to the captive black wire (to feed the 3-position switch). Then the four functions of the ceiling unit are connected to the four switch outputs.

Night light (black) to 3-position switch red (one 'on' position)
Main light (yellow) to 3-position switch blue (other 'on' position)
Heat (red) to one on/off switch screw terminal
Fan (blue) to the other on/off switch screw terminal.

It's not shown which of the 3-position switch red and blue outputs corresponds to which switch rocker direction. You might want to swap those over to get the switch operating in the direction you want.
On that drawing it showed 4 loads and that should be pretty simple to wire. Just listen to Lucien and good look
 

Reply to Wiring a 4-Function, 3-Switch Wall Control in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed...
Replies
1
Views
1K
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
610
  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Hi there, please help. I live in Florida and am replacing a ceiling fan in a bedroom. The new fan has no pull cords and no remote. It came...
Replies
1
Views
1K
Hello, DIYer and first time poster here. Recently bought a house built in 1925, and am gradually working through adding and replacing the wiring...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock