Discuss Wiring garage supply, breaker size recommendations for welder. in the DIY Electrical Advice area at ElectriciansForums.net

S

starmag

Hi guys, I'm planing on putting some power to my grandparents garage so I can work on my car. I'm going to put in one double socket which will be running a freezer, and my welder too, and then a couple 5ft fluorescents or x2 battenholders.. whatever gives the best spread of light?


The thing I'm unsure of which size breakers to use. The garage is detached so the plan was to put in a sub main using a 6mm 3core armoured fed from the main consumer unit on a 63A mcb? Then have this going to a garage consumer unit with a 63A 30mA RCD main switch.. 6A breaker for lights.
Then for the socket, because of the high current drawn by the welder, do I:


1. Type C 20A breaker, radial circuit, 2.5mm
or
2. Type C 32A breaker, ring circuit, 2.5mm

Or do i run a circuit just for the welder socket?

What's your thoughts?

Welder specs below (Clarke 150te)

image_zps0114bdaf.jpg


Any advice is much appreciated.
Thanks, James
 

Attachments

  • image_zps0114bdaf.jpg
    70.1 KB · Views: 39
A 63A MCB on a 6mm cable is a bit hairy for my liking.

Lets start at the beginning, what earthing arrangement is the main house?
 
Yep the 6mm jumped straight out at me ...has the OP missed a 1 of it ?..... If not i'd be inclined to polish the mirror first before you add the make-up.
 
Sorry guys, meant to post this in the DIY section but couldn't? I did my level 2 years ago but never got round to finishing my apprenticeship because the company I was working for went bust, so I'm a bit rusty, sorry
 
No probs, I've relocated it for you.
 
Do your cable calcs to derate the front end mcb of the supply to the garage... best advice is ring manufacturers up regarding mcb sizing i suspect the fuse (20) it relates to could be cartridge style as you may have picked a welder better suited to a workshop not a domestic garage.. again just contact supplier and query this point i may be wrong but inrush current on welders can be high.
 
Thanks Marvo, sorry I missed your question about the earthing arrangement. It's TN-S.

would a 32A be more suited to feed the garage supply?

and as for missing the 1 from the 6mm. What do you mean by that? Surely a 16mm armoured would be a bit overkill? The welder is only a standard plug top
 
Thanks Marvo, sorry I missed your question about the earthing arrangement. It's TN-S.

would a 32A be more suited to feed the garage supply?

and as for missing the 1 from the 6mm. What do you mean by that? Surely a 16mm armoured would be a bit overkill? The welder is only a standard plug top

Not knowing the size of the house, garage or incoming supply all we had to go on was the 63amp mcb you said it had ... 16mm may be overkill but with all due respect the fuse protecting the garage supply is overkill and a fire hazard on a 6mm cable if you developed an high impedance fault.. (overload unlikely in the circumstances of the circuits you listed).

You spec' us a 150TE which is not on the list you posted as the nearest one is a 150T3E on a 20amp fuse but you now say its on a plug top ...conflicting info or you haven't posted the correct spec for your model.

We can only go on what you tell us - be aware we don't know your install except for what you tell us ... i've seen garages before with 16mm ..when you take into account install methods (especially ducting underground) length of run etc etc a cable can easily get to larger sizes even with a 40amp front end device.
 

Reply to Wiring garage supply, breaker size recommendations for welder. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi My main feed comes into the garage, feeds into the meter and then out to another box with a 60AMP fuse then into the house...
Replies
20
Views
3K
Last year we purchased a home that was built in the late 1990s It has one outbuilding, sort of a barn/shed about 160 feet from the house (and...
Replies
3
Views
1K
Hi there. I'm a DIYer. Just bought a house with a double garage that has just one socket in it; and it seems to be just a single spur direct from...
Replies
1
Views
2K
I would like to ask advice on a breaker size. Back in 2001 I turned my garage into a woodworking shop with several 240v machines. To power them I...
Replies
2
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock