Discuss Wiring of Salus RT510RF thermostat to Vokera Compact HE29 in the Central Heating Systems area at ElectriciansForums.net

Reaction score
12
Hi Guys I have an old room stat which is located upstairs in the hallway that I wanted to replace with the Salus RT510RF so I can take it from room to room. I was hoping to just swap it over but I think I will need to run additional cables, if that's the case I might as well just run a standard room stat from the living room to the boiler in the kitchen which is only 2m away. Any comments, recommendations, advise etc would be greatly appreciated as the wiring in the boiler is throwing me a little. Many thanks

20171221_144121.jpg

20171222_131120.jpg
 
Make those cables safe, they will probably have 230v accross them. Then wire in the Salus at the boiler, or airing cupboard using 5 core flex as shown in this diagram;

 
Hi Madocks should I just bypass the timer on the boiler altogether by removing all the cables from the chock & wire COM & ON directly to the chock?

View attachment 40148

I would, let the salus have full control, only concern I have is the little M in the diagram. Not sure what it is, looks like just a feed to the clock but could it be a motor of some sort perhaps? theres only a L&N going to it, but does the internal clock control some motor? label the wires up and fit the salus and see if it works :)
 
I would, let the salus have full control, only concern I have is the little M in the diagram. Not sure what it is, looks like just a feed to the clock but could it be a motor of some sort perhaps? theres only a L&N going to it, but does the internal clock control some motor? label the wires up and fit the salus and see if it works :)
Thanks I will do cheers for the advise
 

Reply to Wiring of Salus RT510RF thermostat to Vokera Compact HE29 in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

i , i have a property to work on which has a programmable room stat upstairs and a programmable roomstat downstairs. S plan system , 2 zones. hot...
Replies
5
Views
399
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
994
Hi. We are looking at installing a Wiser smart heating system inc. trvs We are currently electric only, with normal rads and a Heatrae sadia...
Replies
8
Views
2K
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock