Hello everyone,
I would be happy to hear your opinion about wiring RCBO inside switchboboards, panels. Here I attached some example.
We have 9 (F1-F9) RCBOs, each 20A. If we connect first one (F1) with 16mm2 wire to first phase busbar, second (F2) with 16mm2 to second phase busbar and third (F3) with 16mm2 to third busbar, and neutral with 16mm2 to F1:N, then we can connect everything with comb busbar (L1/N/L2/N/L3/N/L1/N...). Because first phase wire (16mm2) will be enough to supply all first phase RCBOs (F1,F4,F7), 3x20A=60A which is OK for 16A wire. But, what is with neutral wire? The neutral wire in such situation will be undersized? Neutral is the same for
all RCBOs (9 total)....In such way, It looks that we can connect only 3 RCBOs with one comb busbar, because 3X20A is 60A for neutral wire...I would like to hear your opinion..
Shematic.PNG
 
Neutral current is a 3 phase system are not calculated as you think depending on how balanced the loads are across each phase

I'm sure someone here will give a more detailed explanation but in the meantime check out this video which shows you an example waveform and the affects of each phase on the neutral current
 
The neutral conductor should be of the same csa of the line conductors which supply the busbar.
 
Neutral current is a 3 phase system are not calculated as you think depending on how balanced the loads are across each phase

I'm sure someone here will give a more detailed explanation but in the meantime check out this video which shows you an example waveform and the affects of each phase on the neutral current
Thank you, it helps a lot, I also watched the unbalanced neutral and it gives me the answer. Tnx.
 

Reply to Wiring RCBOs inside panel in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
770
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Evening all I’m looking for a little advice here as I have bit of a weird one here. I got called out to a client to look at some computers that...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock