Disconnected a cooker ready for a kitchen to be removed, and found this.
Freestanding cooker with 4 rings, oven and grill.. rated 11.3kW, supplied by what looks like 1.5mm flex.

I know take diversity for cooking appliances, but 1.5 is pushing it a bit.

Just wondered if this was original to the cooker.
Google search on the model no. States 32A

The flex is branded Indesit, which I believe is zanussi, and the ends of the flex are crimped like they belong an appliance.

665870D5-3738-4BAA-82F6-9665E95EB258.jpeg
CB9BAD8F-E1A0-4046-BEE6-FC21C1C3B791.jpeg
4123616E-C8B1-494D-AD34-C5AF399D7FEE.jpeg
 
Considering ho5 can only handle 16a in 1.5 or 25 in 2.5 it may well of been original but probably said something like to be installed on 16a mcb
 
No… it might be 1.00mm. Certainly not 4… which is what I would have used.

you can see the back of the outlet how hot it’s been getting.
 
TBH it looks like its getting hot on the fixed wiring side of that plate.

No thermal damage on that flex Mind you it does look a bit melted down the flex with them ridges

NB cord grip aint doing much like that.
 
Last edited:
I would guess it was from a previous appliance e.g. separate oven of lower rating, re-used this one when the installer realised it didn't come with anything pre-installed.
 

Reply to Would this be original? Cooker flex in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
The never ending debate about supplies for cooking appliances. ??? I've just received an email from a customer that I'm in the process of quoting...
Replies
14
Views
3K
Hey guys, So a customer has bought some fancy 3.35kw combination microwave that comes with a prewired flex of 1.5mm, total load would...
Replies
18
Views
6K
Hi, I would appreciate some views on the following issue I have. The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense...
Replies
12
Views
3K
Went to a job yesturday. 6.6kw 4 ring hob and 4.2kw cooker were both supplied on same 6mm on 32a breaker!! Both still using the 1mm flex...
Replies
29
Views
5K
Stroppy
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock