Discuss would you have thought they would have done this in the UK Electrical Forum area at ElectriciansForums.net

buzzlightyear

-
Esteemed
Arms
Reaction score
7,758
been to a job to have a look at a garage ,where a customer told me is needs sorting ,had a look in the garage and the board hang of the wall.
the customer has just moved in ,and nice new consumer all rcbos for all circuits .now the C88p hang of the wall in the garage is feed from the ring circuit in the house.
and there no test date on that c/u . the DNO system is TN-s. in the garage just below the hang board their is a water services in the garage .now the option is disconnect from the main house ,the cable is 2.5 ,and put in a fresh supply or leave alone and tidy up the garage has it stands.
 
Whats all in the garage that needs a separate db? If its a spur from the house ring, fused down radial circuit. Second SFCU for lighting.
Fix it all up and "remove" the RCBO's and keep them for stock.
 

Reply to would you have thought they would have done this in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
890
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
467
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
749
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
709

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock