I'm aware that 3036's come in Type 1,2 & 3 with different max fault current capacities. What I don't know is how you tell the difference between the Types.
Also, if you assume a Type 1 at 1Ka, what would you code an installation with Type 1 rewireables with a PFC of 1.42Ka? The installation is 40+ years old in really good condition.
Cheers.
 
Guys,
I'm aware that 3036's come in Type 1,2 & 3 with different max fault current capacities. What I don't know is how you tell the difference between the Types.
Also, if you assume a Type 1 at 1Ka, what would you code an installation with Type 1 rewireables with a PFC of 1.42Ka? The installation is 40+ years old in really good condition.
Cheers.

Hi Should be marked sa1, sa2, sa3, its then 1,2,4kA respectively.
 
It can to a certain extent.

The BS88 cutout fuse will limit fault current, in this scenario it will be fine.

I'm just playing devils advocate.
 
It can to a certain extent.

The BS88 cutout fuse will limit fault current, in this scenario it will be fine.

I'm just playing devils advocate.

Hi Rob, i think you were right first time around, at such a low fault level its very possible the peak current will exceed the measured, so in this case if its the SA1 or SA2 the BS88 will not cascade.
 

Reply to Wylex 3036 board - PFC, EICR query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
694
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock