Take a look at these two vids; https://www.youtube.com/watch?v=Bj_plR6lU3o for the wiska gland
and this one from Wylex; https://www.youtube.com/watch?v=XjaEQJBDhts
Interestingly, if you watch this vid' at 4 mins, you'll see that Wylex suggest you can use a 'plastic' time delayed RCD to protect the tails prior to the CU on a TT. My scheme - Elecsa - says NO, and when I rang Wylex (it was in that flyer I posted at the start of this thread), their Tech Support quickly bated me off to some sales person, whom I rang. After a bit of discussion on 421.1.201, he said using such a insulated RCD was the lesser of 'two evils'. I don't think this reg. is going to be completely ironed out for a while.
and this one from Wylex; https://www.youtube.com/watch?v=XjaEQJBDhts
Interestingly, if you watch this vid' at 4 mins, you'll see that Wylex suggest you can use a 'plastic' time delayed RCD to protect the tails prior to the CU on a TT. My scheme - Elecsa - says NO, and when I rang Wylex (it was in that flyer I posted at the start of this thread), their Tech Support quickly bated me off to some sales person, whom I rang. After a bit of discussion on 421.1.201, he said using such a insulated RCD was the lesser of 'two evils'. I don't think this reg. is going to be completely ironed out for a while.