Discuss Wylex Type A or above rcd/rcbo... where to find them? in the Electrical Tools and Products area at ElectriciansForums.net

whats the rcd/rcbo for ? if needed you could put a different brand in an adjacent plastic enclosure, rolec do type a rcbos for around £20 you might have to pay delivery but will be available from most wholesalers. they do 20 and 40 amp versions of the rcbo possibly other rated versions if you look
 
It's for a garage circuit with an EV point taken from the garage board, it's already in place but an EICR identified the AC type RCD isn't suitable. The board in the house is Wylex, put in about 2 years ago, so the simplest thing would be to have a suitable Wylex device to put in there.
 
It's for a garage circuit with an EV point taken from the garage board, it's already in place but an EICR identified the AC type RCD isn't suitable. The board in the house is Wylex, put in about 2 years ago, so the simplest thing would be to have a suitable Wylex device to put in there.
Only the rcd in the charging unit requires to be either a type A or type B rcd.
The supply to the EV charger does not necessarily require rcd protection depending upon the installation method of the cable supplying it and whether fault protection is required by an rcd
You also should not have a type AC rcd upstream of a type A or type B so is that what the issue is?
 
Cheers guys, had a glance at rolec, I think the answer is to modify the installation to take the supply to the EV point off the RCD.

Fortunately for me the supply comes from the main DB to the garage DB is SWA, so I can modify the garage DB to have the other circuits in it on an RCD there. I personally prefer to have it RCD'd from the main board to have the cable run on an RCD too (regardless of it being a requirement or not, original installer was clearly like-minded), but changing that seems to be the only reasonable option here.

A bit disappointed at the difficulty obtaining Type A rcds/rcbos. Even my accessor last time my scam paid a visit made it a point to say we should be looking for Type A due to the type of loads that are commonplace these days, but I can't install what I can't get hold of!

P.S. Thanks Wilko but I'm pretty sure the B type there refers to the mcb (which also makes searching for a B type rcd/rcbo a huge pain as there's a ton of unwanted results).
 
A bit disappointed at the difficulty obtaining Type A rcds/rcbos. Even my accessor last time my scam paid a visit made it a point to say we should be looking for Type A due to the type of loads that are commonplace these days, but I can't install what I can't get hold of!

P.S. Thanks Wilko but I'm pretty sure the B type there refers to the mcb (which also makes searching for a B type rcd/rcbo a huge pain as there's a ton of unwanted results).

Hi - agree, these RCBO are type A RCD with a type B or C mcb.
 
At a better price again, but sadly you never returned my email last time!

Hi Matthewd29,

I'm sorry if we've missed an email from you.

If you have any enquiries feel free to message directly on here and I will make sure it's followed through.

Cheers,
Ivan
 

Reply to Wylex Type A or above rcd/rcbo... where to find them? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
916
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Hello all.. I'm quoting for some work and would like change the type AC RCBO to a type A. Consumer unit is a castlec which I have not come...
Replies
5
Views
917
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock