Anonomoose

Hi, Wondering if anyone can offer me some advice. I've just gone to a job to relocate and wire a new cylinder stat for a pressurised system. I wired it all in but could not get the central heating to work without the hot water being off. I spent a bit of time checking and couldn't figure it out as it was all done right (or so I thought) the existing wiring was a bit of a mess so after a bit of tinkering I thought it would be easier and quicker to rewire the whole system. After a lot of swearing and cursing I have been left with the same problem. no central heating without the hot water being switched off. Any help greatly appreciated as im all out of ideas.


Paul
 
When you say pressurised system, do you mean a sealed system in terms of the primaries/heating or do you mean an unvented (mains pressure hot water) cylinder?

What happens if the hot water channel is on and the heating off with the cyl stat on?
And the same with the cyl stat off?

What happens with both channels on and the cyl stat on and room stat on?
Now the same but with the room stat off?
And with both channels on, room stat on and cyl stat off?

And now with the hot water channel off and the room stat on?
And the same with the room stat off?

You need to follow this logical process of each combination of the controls and taking note of what the valve and boiler does with each change of the controls.
Then just compare this to what should happen at each change of the controls and you should be able to establish what is or is not happening.
 

Reply to Y plan help in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K
Hi I'm in a bit of a pickle trying to set up my hot water and central heating systems. Got a gas boiler with a pressure tank and a motor...
Replies
7
Views
911
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
620

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top