Discuss You need scrambled brains to sort this! in the Commercial Electrical Advice area at ElectriciansForums.net

Well done Lenny, I couldn't even work out why there were breakers in the earth or whether there was a neutral connected at all!
Thanks for the diagram Tony one massive amount clearer than the "description"
 
Tony's diagram shows exactly why you should never have 3 pole ACB's and solid neutral on dual feed switchboards!!! This problem would never have occurred if all the ACB's were 4 pole.... Same situation occurs when you have a stand-by generator included in the switchboard arrangement, using 3 pole ACB's (breakers). The stray neutral currents fly all over the system unbalancing and tripping out any earth fault relay protection incorporated on the system....
 
the diagrame makes it 100%understandable but im glad i stick to 400v stuff n leave the higher stuff for those who know what they are talking about
 
It’s not just ACB’s as E54 pointed out, but many switches have a removable neutral links. It’s all to easy to overlook refitting them after testing.
In the drawing the most important link that should have left in was the one between the two transformer sections.
 
It’s not just ACB’s as E54 pointed out, but many switches have a removable neutral links. It’s all to easy to overlook refitting them after testing.
In the drawing the most important link that should have left in was the one between the two transformer sections.

If the ACB's were all 4 pole, then the only removable links on the system would be the two N-E links between the N and E bus bars. (Earth bar not shown on the drawing)

But if the system installed is as in the drawing, then yes the links will be everywhere on a 3 pole breaker + solid Neutral system...
 
the diagrame makes it 100%understandable but im glad i stick to 400v stuff n leave the higher stuff for those who know what they are talking about

Err, ....this ''IS'' all 400 Volt stuff!!! Only untill you get to the other side of the TX's will you be in MV territory!! ...lol!!!
 
I suppose the beauty of the systems I’ve worked on is you would never come across earth fault protection until well away from the main boards. All the transformers had REF obviously. The main neutral at the transformer switchboards were always kept continuous, links were removed for dead testing only.
RCD’s were as rare as hen’s teeth. About the only place you would find them would be in the few sockets used by the conveyor belt vulcanises, these had to have pilot/earth monitoring as well.
It was a shock to the system when the portable tool rules were relaxed to allow 110V, previously it was 50V centre tapped. Portable welding plant was unheard of, it had to be fixed or diesel.
Just before I came out of my time I was working in the contracts management office, I had fun! Can we use…… NO! What about….. NO! Suppose we can’t use the bloody kettle can we? NO, plenty of fixed mashing urns about the site, you use them. I was only applying the rules, but I made a meal of it.
The first computers on site caused chaos. We found a way around that eventually by getting the M&Q inspector to issue dispensation for offices. Then came the plant control rooms, it got messy. The 20[SUP]th[/SUP] century caught up with us in the end. Things changed from trying to find ways round the rules to applying them.

PS the earth bars are on the drawing.
 

Reply to You need scrambled brains to sort this! in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock