Discuss Your opinions please in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
211
I got called out to price up some additional socket outlets for a customer. As I walked around checking things out I could not locate the Main Bonding to the water supply. I pointed it out to the customer, whos reply was "oh I think the kitchen fitters electrician did that, I will ask him". I told them he has bonded the gas, but the water hasn't been done.

Anyway a few days later they send me an email with the minor works certificate attached. Not the first time this has happened, but it does annoy me :mad:

View attachment 35343

View attachment 35344
 
Having done a few kitchen refurbs myself, I've ensured the water service is bonded and has continuity, only to return for 2nd fix to find the kitchen fitters have hidden said bonding behind the floor unit.

Tried educating kitchen fitters no end, seen some that have even hid the water stopcock behind the floor unit. Did bonding accessible behind removable plinth on one job, only to be told off by my scheme assessor, that that was not accessible.

Luckily for me now, I predominately do work for the same kitchen company, where I've educated the fitters. We either have all the pipe work/bonding accessible in floor unit, or drill a large diameter hole in the rear of floor unit where bonding point is easily accessible. :cool:
 
Last one I found with no water bonding was a new installation and the Previous Guy had left that bit of EIC blank. It turned out it was ok but a note on cert would have saved me testing :) .

Maybe there was quick visit from Previous Guy to fix "and btw, since I'm here ..."? Not much fun for you
 
More info needed. Can you see the incoming water service? Are you certain it requires bonding?

Yes I can see it and it does require bonding, there's a hole cut in the rear of the base units to access the stop cock.

Theres only one 10mm2 conductor running from the met to the gas & that's as far as it goes.

The description on the certificate is a bit vague, I always like to put as much useful info as possible so anyone coming in after me has a clear picture.

There's other issues too but that's another thing.
 

Reply to Your opinions please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A friend of the family recently lost her husband to the big C so I need to be careful. Every small thing is sending her into tears so when her...
Replies
16
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
479
I'm starting a new project on Monday, new dental practice conversion from a shop. Nothing new here, customer doesn't know what electrical heating...
Replies
12
Views
743
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
863
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock