Discuss ZE at board/earthing alternatives in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

StokieSpark

Hi there... Couple of questions for you experts. Still learning.....:eek:

Been to a factory today... It has one main incoming board and 55 distributon boards scattered around there factory...

They asked me to fit/wire a couple of socket outlets under one dist board. Which only uses the armoured of the SWA as an earth but the phase conductors are 50mm2 each and i was under the impression that you can only use the armoured strands for an earth for cable upto 25mm2 (Is this right? )

As a result i measured the Ze and it measured in at 0.99ohm, (The factory is TNS) so the maximum i can have is 0.80ohm right?
I then measured it at the incoming board and it measured 0.19ohm, which is fine.

So I phoned my boss and told him we need to run a separate earthing conductor, he told me to just take a earth off the closest steel girder and that will be good enough..

Im not convinced... Surely the DNO supplied an earth for a reason and not used rods? And would this turn the installation into TT????


Give me your expert feed back. Thanks.
 
Hi.

A bit confused, an installation can only have one Ze, at the origin....I assume this is your 0.19 value??? The 0.99 value is a Zdb I'm guessing (Zs of sub-main circuit).

What sort of length is the sub-main circuit, and are there earth leads present from the earth tags of the SWA glands to the earth terminals and are the glands sound???

The armour is fine to use as the CPC for the sub-main as it has a copper equivalent of about 32mm.
 
Sorry I dont speak the lingo.

Yes Ze at the incoming is 0.19 and the Zs at the submain is 0.99.

It is rougly 120M away.

The gland is all fine, earth lead from the banjo and all nicely tight.
 

Attachments

  • Untitled.jpg
    4.6 KB · Views: 35
Taking that into account, I can see no reason why you cant install your additional sockets, They will need RCD protection IMO, unless they are for specific items etc etc, even then the Zs may push you over the maximum for an MCB anyway.
 
Your Boss might want to have a think about it,run an earth to the nearest steel girder?...is he for real?
maybe his boss didn't realise that there is a water pipe close by ( only joking)
 
I was "taught" that all submain boards must be under the 0.80ohm(tns systems)
I didnt know that it would come under the 'max Zs'


Its like the blind leading the blind where i work!
 
What type and size of overcurrent protection is on the sub main as this might make the 0.99 value exceed the max permissible Zs.
 
Are you sure......Stevie's asking about the fuses/MCCB protecting the 50mm SWA sub-main now, not the main incommer fuses.

Max Zs for a 160A BS88 is 0.25ohms.
 
Indeed as Lenny says it's the protection on the sub main not the incomer.
 
Right, the main incoming is a Giant MCCB is 800A which goes too a "cupboard distribution board" next to it, with a 160A MCCB which feeds the submain that has 150A BS88 main fuses.MCCB.jpg
 
You can't get a 150A BS 88 as far as i know 125A then 160A
 
Going back to the bosses comments it is permissible to use an extraneous conductive parts as protective conductors.....I don't make the rules.
543.2.6.
I think there would need to be a bit more investigation than "just take an earth from the nearest girder"
P.S. I have never done it and hope never to have to.
I'm going to hide from the bullets now.:D
 
No probs mate but regardless the Zs on your sub main is way to high for the 160A MCCB protecting it.
 

Reply to ZE at board/earthing alternatives in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
725
Hi, My son has just (last week) had a rewire done on his house in Leyland. He has just bought the house but a "domino" type consumer unit was...
Replies
149
Views
12K
I've just started at a new church and the electrics are bit of a shambles. I'm not going to be touching them as I'm not qualified, but one thing I...
Replies
14
Views
5K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
Hello All Strange question for you, I know you don’t have crystal balls :) but can anyone give me any clue on the following… I have mid eighties...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock