0.01ohms? Does this comply? Tns system. Unsure because, usually given as 0.8ohms, previous test cert gives 0.08 ohms. Not sure if previous spark rang supplier or just put 0.08 anyway. Is this value ok anyhow?
 
Last edited by a moderator:
max. value is 0.8ohms. 0.01 is low. what's your measured PEFC?
 
The max value for a TNS is 0.8 ohms so anything less is fine. Although at 0.01 ohms you must be on top of the supply transformer.
 
0.01ohms? Does this comply? Tns system. Unsure because, usually given as 0.08ohms, previous test cert gives 0.08 ohms. Not sure if previous spark rang supplier or just put 0.08 anyway. Is this value ok anyhow?

You're worrying me, is this a periodic inspection?

The agreed maximum Ze on a TN-S system is 0.8 Ohms.

0.08 Ohms could well be correct but because of your meter's inaccuracy at these values due to 'second-digit tolerances' it's difficult to measure.

0.01 is virtually impossible once transformer windings and distribution circuit impedance is considered.
 
0.01 would give a PFC of 23kA, ignoring parallel paths.. that's why i asked for the measured value.
 
Sorry guys yeh value I was getting was 0.01ohms. PFC was about 23ka telectrix, dodgy instrument? Due for calb in a month all other test have been fine
 
well. your pfc matches your Ze. can't see the test meter being far out on both scales.
 
0.01ohms? Does this comply? Tns system. Unsure because, usually given as 0.08ohms, previous test cert gives 0.08 ohms. Not sure if previous spark rang supplier or just put 0.08 anyway. Is this value ok anyhow?

Electricalserv, was the job in the sleeping quarters of a self contained unit in an electrical sub station for overnight staff :p
 
well. your pfc matches your Ze. can't see the test meter being far out on both scales.

The problem is, the meter is using the same method to determine both Ze and PFC.

The instrument has to be accurate to 0.05 Ohms (5%) when measuring impedance but at readings below about 0.5 Ohms, this accuracy pales.

This is down to second digit tolerance which can vary between 4 and up to 10.

A meter reading of 0.05 Ohms with a meter of tolerance +/- 2% (+/- 4 digits) could actually be measuring a true value of between 0.01 and 0.09 Ohms.

Do the maths as the meter does to work out a value for PFC and the discrepancy is massive.
 
Its quite possible to have a pfc that high especially if the transformer is nearby.

It is theoretically possible to approach values above 16KA but in practice, it's almost unheard of.

Since becoming aware of the scenario that I described in post 11, any conventional Ze measurement that we find below 0.10 Ohms is re-measured with an adjusting impedance added to lift the meter into it's acceptable range (normally above 0.30 Ohms).

The difference always makes this a worthwhile 10 minute exercise and shows how poor our meters are at values below 0.30 Ohms.
 
It is theoretically possible to approach values above 16KA but in practice, it's almost unheard of.

Well if you have a 1000kva transformer, using a transformer impedance of 4.75% you would get 30.5ka at the terminals, so if your close to the transformer a high PFC is possible.
 
Well if you have a 1000kva transformer, using a transformer impedance of 4.75% you would get 30.5ka at the terminals, so if your close to the transformer a high PFC is possible.

Absolutely right but from my point of view as a serial measurer of Ze, I have yet to actually measure a value of Ze low enough to give a PFC higher than 16kA
 

Reply to Ze at origin tns in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock