Search the forum,

Discuss Ze at origin tns in the Australia area at ElectriciansForums.net

E

Electricalserv

0.01ohms? Does this comply? Tns system. Unsure because, usually given as 0.8ohms, previous test cert gives 0.08 ohms. Not sure if previous spark rang supplier or just put 0.08 anyway. Is this value ok anyhow?
 
Last edited by a moderator:
max. value is 0.8ohms. 0.01 is low. what's your measured PEFC?
 
The max value for a TNS is 0.8 ohms so anything less is fine. Although at 0.01 ohms you must be on top of the supply transformer.
 
0.01ohms? Does this comply? Tns system. Unsure because, usually given as 0.08ohms, previous test cert gives 0.08 ohms. Not sure if previous spark rang supplier or just put 0.08 anyway. Is this value ok anyhow?

You're worrying me, is this a periodic inspection?

The agreed maximum Ze on a TN-S system is 0.8 Ohms.

0.08 Ohms could well be correct but because of your meter's inaccuracy at these values due to 'second-digit tolerances' it's difficult to measure.

0.01 is virtually impossible once transformer windings and distribution circuit impedance is considered.
 
0.01 would give a PFC of 23kA, ignoring parallel paths.. that's why i asked for the measured value.
 
Sorry guys yeh value I was getting was 0.01ohms. PFC was about 23ka telectrix, dodgy instrument? Due for calb in a month all other test have been fine
 
well. your pfc matches your Ze. can't see the test meter being far out on both scales.
 
0.01ohms? Does this comply? Tns system. Unsure because, usually given as 0.08ohms, previous test cert gives 0.08 ohms. Not sure if previous spark rang supplier or just put 0.08 anyway. Is this value ok anyhow?

Electricalserv, was the job in the sleeping quarters of a self contained unit in an electrical sub station for overnight staff :p
 
well. your pfc matches your Ze. can't see the test meter being far out on both scales.

The problem is, the meter is using the same method to determine both Ze and PFC.

The instrument has to be accurate to 0.05 Ohms (5%) when measuring impedance but at readings below about 0.5 Ohms, this accuracy pales.

This is down to second digit tolerance which can vary between 4 and up to 10.

A meter reading of 0.05 Ohms with a meter of tolerance +/- 2% (+/- 4 digits) could actually be measuring a true value of between 0.01 and 0.09 Ohms.

Do the maths as the meter does to work out a value for PFC and the discrepancy is massive.
 
Its quite possible to have a pfc that high especially if the transformer is nearby.

It is theoretically possible to approach values above 16KA but in practice, it's almost unheard of.

Since becoming aware of the scenario that I described in post 11, any conventional Ze measurement that we find below 0.10 Ohms is re-measured with an adjusting impedance added to lift the meter into it's acceptable range (normally above 0.30 Ohms).

The difference always makes this a worthwhile 10 minute exercise and shows how poor our meters are at values below 0.30 Ohms.
 
It is theoretically possible to approach values above 16KA but in practice, it's almost unheard of.

Well if you have a 1000kva transformer, using a transformer impedance of 4.75% you would get 30.5ka at the terminals, so if your close to the transformer a high PFC is possible.
 
Well if you have a 1000kva transformer, using a transformer impedance of 4.75% you would get 30.5ka at the terminals, so if your close to the transformer a high PFC is possible.

Absolutely right but from my point of view as a serial measurer of Ze, I have yet to actually measure a value of Ze low enough to give a PFC higher than 16kA
 
Well here you have it. Nulled leads etc. Remeasured 0.02 ohms 11.5ka 20m from substation. This is the house my bro has just bought. Previous test result was 0.08 ohms so very low aswell.....
 
Last edited by a moderator:
It is theoretically possible to approach values above 16KA but in practice, it's almost unheard of.

Since becoming aware of the scenario that I described in post 11, any conventional Ze measurement that we find below 0.10 Ohms is re-measured with an adjusting impedance added to lift the meter into it's acceptable range (normally above 0.30 Ohms).

The difference always makes this a worthwhile 10 minute exercise and shows how poor our meters are at values below 0.30 Ohms.

i regularly find high pfc readings iq, had one recently.01 ze off the scale ipf. what would be your course of action in that situation?
 
i regularly find high pfc readings iq, had one recently.01 ze off the scale ipf. what would be your course of action in that situation?

No, your meter displayed a reading of 0.01 Ohms, read back through the thread, the bit regarding 2nd digit tolerance, it makes a massive difference to PFC as you can imagine when a Ze reading can be between 0.01 and 0.09 Ohms.

The only way to increase accuracy at those levels is to use a known resistance in series to lift the meter into it's 'sweet spot' accuracy area.

I wrote a piece on how and why to add the resistance, I'll find it following my house move and get it posted up.

If you do a lot of testing, it's well worth doing this 10 minute procedure.

Out of interest, check your meter's quoted accuracy range-a Megger 1553 is >0.30 Ohms!
 
will do iq. i think any ze above .12 is high tho lol. city centre edinburgh. please pm me with your piece on how and why to add resistance.
 
You can always calculate the Ze at origin, like we used to have to do, before Loop Testers were around!! Get an accurate volt meter and a load of around 40 to 50A. Measure the voltage at no-load, and then with the connected load, there will be a voltage drop. Whatever the voltage drop difference measured, divide by the current you applied, ...that's your value!!! You can then go onto find the PSC by dividing the no-load voltage, by the figure you attained above....

At the very least it will give a good indication if your meters measured value, is anywhere near accurate. Your only problem being, ...is providing a known current load to measure the volt drop. We used to have home made load banks, that we made as part of our training. But any steady load can be used of sufficient current to cause a volt drop at the origin of your supply.
 
Last edited by a moderator:

Reply to Ze at origin tns in the Australia area at ElectriciansForums.net

Similar Threads

Hi, first question on here in a very long time, I am hoping for some nice replies ?. It's been playing on my mind all week and can't seem to find...
Replies
12
Views
4K
Im currently in a dispute with UK power networks about who is responsible for the incoming earth? Now, i know under normal circumstances the owner...
Replies
13
Views
5K
D
Carrying out a few minor remedials following an EICR on a small rented cottage this morning. One item was to replace the immersion heater stat for...
Replies
19
Views
3K
NICEIC Certification Scheme NICEIC approved contractor first visit
Info for anyone currently looking to join, Whilst I was very nervous the night before, there is no need to be, as long as you know how to test...
Replies
18
Views
10K
N
Anyone care to comment on my reasoning, calculation and conclusion here? I'm doing an EICR on a TNS system, with copper 4mm2 DNO earthing...
Replies
2
Views
886
NickD
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top