Discuss Ze Values? HELP in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

0.80 implies greater accuracy than value than 0.8

Could it be that it was 0.8 exactly, with the zero dropped as it would be irrelevant, to the outcome calcs.
Sorry I'm trying to get my head around this, not disrespecting your post.
 
Could it be that it was 0.8 exactly, with the zero dropped as it would be irrelevant, to the outcome calcs.
Sorry I'm trying to get my head around this, not disrespecting your post.

The zero is relevant to the outcome of the calculation as it will have an impact on its accuracy.
0.8 x 0.320 = 0.3
0.80 x 0.320 = 0.26
0.800 x 0.320 = 0.256

0.8 is a value anywhere between 0.75 and 0.84 wheras 0.80 is a value between 0.795 and 0.804
 
The zero is relevant to the outcome of the calculation as it will have an impact on its accuracy.
0.8 x 0.320 = 0.3
0.80 x 0.320 = 0.26
0.800 x 0.320 = 0.256

0.8 is a value anywhere between 0.75 and 0.84 wheras 0.80 is a value between 0.795 and 0.804

...Your calculator needs re-calibrating...:icon12:
 
Could it be that it was 0.8 exactly, with the zero dropped as it would be irrelevant, to the outcome calcs.
Sorry I'm trying to get my head around this, not disrespecting your post.

Yes mate. If the 2nd, 3rd 4th etc decimal place is not required, dont need to use it or it would become 0.800000 or 0.8 X 10 to the power of minus 6 :wink: (level 3 maths, you will see)

^^ that is correct isn't it gents? Been a long time since writing this form of equation and it does not look right?
 
This is getting too in depth,anyone know if my maths are right,I seem to keep getting e=mc squared
icon11.png
 

Reply to Ze Values? HELP in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
952
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Cable calcs using cable calc app Working out cable size for a workshop. 100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock