They do it cause some people want it and it is an extra feature that other testers don't have.
Discuss Ze - zs = r1 + r2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
They do it cause some people want it and it is an extra feature that other testers don't have.
No not really, if you had a gun you dont have to shoot someone with it. At the end of the day, as a qualified electrician, you can put whatever you deem fit in the R1 + R2 box, it is only a model form taken from non statutory regulation.So at the end of the day even though its bad practice its still acceptable to the powers that be?
Thanks for your replies, I'm in a protracted discussion about this subject and the people involved are using the fact that the meter
has the facility makes it acceptable practice. I disagree for all the reasons given in this thread.
I measured a Ze on a TT the other day and it was 197Ω, Zs on the ring was 73Ω so by using Ze - Zs = R1 + R2 I get an R1 + R2 of -124Ω that's a damn fine conductor!
I can't see how it could ever be acceptable to calculate R1+R2 this way.
well spotted, hawkeye.Is the title in this thread wrong? Shouldn't this (unacceptable) practice be Zs - Ze = R1 + R2
well spotted, hawkeye.
I have a 1720 myself. I know there are sparks who do calc Zs (Zs-Ze=R1&R2), but it can potentially be very inaccurate when you take into account parallel earth paths. The megger is basically doing this for you and it encourages the bad practice.
Do you disconnect all the parallel paths when measuring then??
Bad practice my arse.
of course it's bad practice. R1+R2 should be measured before the circuit is energised. otherwise, how do you ensure that it's safe to power up?Do you disconnect all the parallel paths when measuring then??
Bad practice my arse.
of course it's bad practice. R1+R2 should be measured before the circuit is energised. otherwise, how do you ensure that it's safe to power up?
Indeed you could. We can both pretend that this is a very current thread.Hello
I may be simple missing something here but if you put a link in at the board to measure your R1R2 and test at the last point. Surely you could still get a parallel path measurement. As the earth is connected to the met at the board. Or is that simple incorrect. As a z's is testing the earth loop and not just a low ohs resistance test?
Well it was just the most relevant one. So what if you can explain is the difference then between measuring the parallel path with a Z's as opposed to the R1+R2?Indeed you could. We can both pretend that this is a very current thread.
Are we suggesting that one should really remove the cpc and test the circuit individually. Otherwise I am still in the dark as to why the parallel path causes an issue for one test but not the other.Well it was just the most relevant one. So what if you can explain is the difference then between measuring the parallel path with a Z's as opposed to the R1+R2?