Hi

When filling in an Schedule Of Test Results, the top left box asks for ZS at DB.

On an installation with only one DB will the ZS at DB recorded as the same value as ZE.

After performing a ZE test can you reconnect the Earthing conductor and test for ZS and use that value.

Parallel paths will occur ?

Thanks
 
The PFC is usually highest at the origin of the circuit/supply. Hence Ze is used to calculate this. I would not be putting Zs at DB for the origin CU. I noticed that my iCertifi has also changed this from Ze to Zs which has puzzled me. Has something changed in regs? Am I missing something?
 
Last edited:
Ze is the external fault loop impedance of the supply characteristics carried out with the main earth disconnected.

Zs is the internal fault loop impedance and external fault loop impedance combined with the main earth connected, I don't see how you can transpose one with the other, they are two entirely independent measurements. Or am I missing something?
 
Did not think I would ever disagree with JW, but in his video above at 29:21 he states that the Zs at DB on the test sheet is for an additional board not the main board as detailed previously on a different page, yes you have repeated the information, but it allows the test sheet to stand on its own, the point is it's the main board test sheet not a supplementary board, IMO you append an additional test sheet with the full details of DB2 under "DB reference no" if needed.
 
Last edited:
It could be a case of differing interpretation.
I generally don't have the time or patience to watch such a video ....for three quarters of an hour. Looking at that particular certificate at the half hour point, as you say, It does look that way (he knows his stuff but he ain't half boring).
However, with NICEIC certs, there is the 'only if connected directly to the origin' factor, a good point, I feel.

IMG_1133.jpg
 

Reply to ZS AT DB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
637
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
3K
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top