Discuss Zs on TT in the UK Electrical Forum area at ElectriciansForums.net

the point is that there are 3 points.............. one on each of your test leads. also, you need to measure the Zs to ensure that it's below 1667 ohms ( 30mA RCD) or 500ohms (100mA RCD).
 
Do you understand what I'm saying?

again for the brain impaired.

what is point in zs test on TTsystem , that has 100mA rcd and Ra of 14 ohms

And there was me proudly boasting on another thread that if the 'celt' boys came to England the electrical competency there would be hugely improved .....
 
Me !:38:, Me no speaky English , me no commit to big can of whoopass !!!!
But having said that , I think I can understand what you trying to say !?
 
.... you need to measure the Zs to ensure that it's below 1667 ohms ( 30mA RCD) or 500ohms (100mA RCD).

Tel, dont be giving him solutions ....... tease it out a bit longer and make him think! Ooops, what am I saying, hes a "Celt" boy, supposedly electrican finest breed :wink_smile:
 
all i can say is that they must have a stronger variety of weed in scotland than he's used to the irish stuff. :dupe:
 
I was going to write a silly answer but I gave up because I couldn't make it as silly as the question. Can you rephrase?

I read it as: Why test Zs on a system where the Ze is much higher than the Zdb? Or maybe: 'Why test Zs when the results are going to be high but not too high.' Either way it's pretty wacky.
 
This one is a serious contender for 'thread of the week' award, I've had tears rolling down my face whilst reading it.

I assume Mr I=PU is asking why is the Zs relevant if you know the Ra is good enough to meet the required earth impedance on its own without the assistance of parallel paths.

Okay, I'm going to let the English who apparently 'are slow' and allegedly 'on the ale' sort this one out ;)
 
This one is a serious contender for 'thread of the week' award, I've had tears rolling down my face whilst reading it.

I assume Mr I=PU is asking why is the Zs relevant if you know the Ra is good enough to meet the required earth impedance on its own without the assistance of parallel paths.

Okay, I'm going to let the English who apparently 'are slow' and allegedly 'on the ale' sort this one out ;)

Don't forget that we are all apparently Gay as well ! :shocked3:

Edit; According to another thread at the moment that is !
 
looks like i`v missed a few good opportunities this evening to have a go..

got called out to a faultfind which turned out to be several neutral-earth faults...

and yep....the RCD was tripping...

it aint now though.....;)
 
No glen not have a good go, no no no , support what I am saying.

if you have ze of 14 ohms what is the point of doing zs test , as you know your readings are to high for protective device already.


Brains just ain't your friend last two days guys , AAA?
 

Reply to Zs on TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
486
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
445
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock