- Reaction score
- 649
Fitted 2 new external lights onto existing cabling, their on a remote wall quite a distance from house.
My mistake was not doing a Zs before I started the works.
Finished & tested Zs reading 14 ohms.
Its a Tncs supply quite a big install…the lights are supplied by a 6 amp C type MCB.
Reported this to the Client & my Boss…still no feedback on what to do.
I”ve suggested a Rcbo to protect this circuit & FI TO take place.
Windering your thoughts on this.
My mistake was not doing a Zs before I started the works.
Finished & tested Zs reading 14 ohms.
Its a Tncs supply quite a big install…the lights are supplied by a 6 amp C type MCB.
Reported this to the Client & my Boss…still no feedback on what to do.
I”ve suggested a Rcbo to protect this circuit & FI TO take place.
Windering your thoughts on this.