Discuss Zs reading high! in the Australia area at ElectriciansForums.net

first compare it with another meter if you have a mate with one. i would still be inclined to suspect MCB or RCD is adding that 0.7 ish value.
 
MCBs have to have some impedance in them... for the heating element that bends the bimetal for the low%, long duration overload and of course the electromagnetic trip coil.
In practice, the small amount these add to the measured Zs is negligible, as the resistances are inversely proportional to current rating.

I have found a good number of RCDs that add significantly to Zs values though. BG is one of the brands that spring to mind.
Yet most brands don't.
I have a bit of a theory though.
Think about how an RCD operates, it's a transformer with two primaries 180 degrees out of phase, so if what goes out down Line comes back down Neutral, the magnetic flux and therefore the inductance cancels out (you've just got winding resistance) and importantly, there's nothing coming out of the secondary.
But under the Zs test, you're causing a deliberate imbalance. Therefore there will be a measurable inductance, it is this which adds to the system impedance Zs.

I had one last week - a SFCU for a boiler. 20A Radial circuit, 2.5/1.5T&E 1m long.
Nice beefy TN-S supply, Ze 0.07 Ohm, PFC 3.9kA
(R1+R2) 0.01 Ohm.

Was the Zs 0.08 Ohm? No. It was 0.57 Ohm.
Testing on the supply side of the RCD got a Zs of 0.08 - but on the load side 0.53 Ohm - both on No Trip setting.

Simon.
 
Thanks for the replies guys.
Absolutely right Rockingit. I will not be happy having spent £500 on a new Megger if I can't trust it's readings, or get readings that are above the max Zs allowed by BS7671 when it shouldn't be. Yes there are tolerances for test results but +/- 5% not + 250%.
To clear up a couple of matters the supply is TNCS, the length of cable is about 20 metres (8 metres of 6mm T+E inside cavity wall upto loft, then into 60 amp juntion box joined to 10mm through isolator to shower.) Yes 0.91 is just OK for the 40 amp MCB but it's very close.
As I said earlier I also got high readings on the cooker circuit 101 when it should have been 0.32 and radial sockets 106 should have been 0.53.
I'm starting to think I may need to send the meter back to have it checked.

The no trip test on the new 2 lead meggers IS totally unreliable....do 10 tests on the same point and you will get 10 different readings. I sent my megger back after a week,and it came back saying nothing was wrong....they even suggested I didnt know how to test. I understand the point about resistance through RCD's affecting it,but given that it is designed to be used on circuits with an RCD this is hardly a valid excuse.Now I just factor in it's unreliability,use it with a combination of the expected calculated result to 'average' it out....if possible do several Zs tests and take an average from them. But as malcolm states dont lose any sleep over it.
 
Last edited by a moderator:
Yes the board and RCD, MCB's are cheap Control Gear from Denmans, so quite possibly high impedance through the MCB's.
Interesting to hear from wirepuller that you were also concerned about your new Megger and sent it back for testing. At least I'm in good company if do the same. Mine is a combined loop and RCD tester with 2 wire Hi current loop test, but does require 3 wires for no trip test. It's pretty C**P if the supposed best meter manufacturers can't make a no trip meter that gives correct and reliable results.
 
My Metrel does this, always way higher on Notrip function, presumed it was the resistance through the RCD but have to be honest, think its pretty pants that they cannot somehow offset the result (not sure how myself mind!) I was going to ask a similar question the other day about it actually but forgot, seems all the MFT's suffer from this then?
 
its the silly 15mA test..

back to college days when doing R1+R2 testing, you start off at say 2000 ohms get high reading, then drop scale too 200 ohms and get better reading, then drop scale too 20 ohms and get better reading again..

pretty much the same, your imitating a fault but not the same fault you need to dissconnect the mcb..
 
your using the no trip setting for the zs at the shower? what are the readings for the zs at the board if you use it on no trip. I know with my fluke that readings on no trip are considerably higher than on normal setting
 
Ok, so on the basis that all MFT's appear to give higher results on notrip setting, which result would you record? (R1+R2)+Ze or notrip Zs ? Are there any other options as otherwise its going to look like you've got a resistive terminal somewhere on the test certificate, or would you note that test was carried out using notrip facility and given the fact that an RCD is present the disconnection times are satisfactory?
 
It is acceptable to put a measured Ze + a measured (R1+R2) and a calculated Zs on your sheet, what is not acceptable is to use a 'ball park' Ze (not measured, or obtained by enquiry) and calculating your Zs from this.

Like others my 'No trip' readings are always slightly higher, but I still take the reading to make sure it is close to my calculated/expected Zs (see above), but I don't record this, I do as in the previous paragraph above (calculated.)
 
Last edited:
Thanks sparks68 that seems to be the most logical way around the problem and it is what I have done in the past. I always take a measured Ze even though most of the documentation seems to state Ze (by enquiry) which seems odd and from reading previous posts on here, most likely impossible!

Why you would not measure Ze I don't know, it would surely take longer to phone up than to disconnect the main earth and attach the test leads?
 
Never been in that situation so yeah I can see there being times where it is not practical to do so, but even so that would normally be in more exceptional circumstances from the average sparks I would guess? Still I can't see any reason for documentation refering to Ze by enquiry as if it is the prefered option?

Or am I reading into it wrong?
 
Most certs i think are designed for all situations and there is always the chance one turns up one day, but your right domestic has no reason at all and it is rare other than ind/com.
edit
should say, remeber certs are based on models shown in 7671 so i doubt they can deviate
 
Last edited:
Its quite easy, i believe, to check your resistance values without spending a fortune on expensive test-check boxes.You can buy resistors for a matter of pence from Maplins get a selection high & low values.
 
just what i did last year, but, like a lot of bits, lost in the garage till tidy up time.
 

Reply to Zs reading high! in the Australia area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
309
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
989
Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I...
Replies
27
Views
7K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock