Discuss Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net
stupid thing any body can do ,op where you going to rely on the bonding .Also why is the installation energised with the main earth disconnected
If you have main earth disconnected , surely it would be ZE not ZS.? (at source)
Parallel path via CPC to boiler circuit CPC to boiler manifold to pipework within the fabric of the building?
Also why is the installation energised with the main earth disconnected?
Parallel path via CPC to boiler circuit CPC to boiler manifold to pipework within the fabric of the building?
Also why is the installation energised with the main earth disconnected?
[/QUOTE
working on the HIGGS BOSON PROJECT.Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
You can’t make an omelette without breaking a few eggs.....Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.
Thanks for that post really helpful!Why do this as a live test when that means doing something as stupid as energising the installation with the earthing conductor disconnected?
Electricians are supposed to understand the fundamental principles of electrical safety!
I understand that but my MFT has those two choices. The KT63 has a piggy back lead that you place the earth lead into to test across L-N I am not truly sure of the purpose of this but there it is. Perhaps you could shed some light on that?Zs is line to earth external impedance, it stands for nothing else.
Depending on circumstances, main earth may need to be disconnected to verify certain fault conditions..
All comes down to knowledge, understanding what is going on and being in control of the location.
Of course there is PSCC and PEFC which I also understand before you go there. I know I should have said loop test. Or PFC PSC even
Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.