So you've got a circuit with a CPC present in at least one fitting, but no CPC present at the DB, and you want to find out where that CPC is getting its earth from, to decide whether it's trustworthy?

If it were me, I'd turn the board off, maybe separate out the CPCs, null out a nice long wander lead, clip the end of it on the CPC and probe various likely contenders around the house with the meter on low ohms, to see which gives the lowest reading and hence is the likely tap off point. I can't see any advantage investigating this live, but many disadvantages.

Or, since it's at least a bit of a bodge, maybe a lot of a bodge, declare the circuit CPC-less and treat accordingly.
 
Zs is line to earth external impedance, it stands for nothing else.
I understand that but my MFT has those two choices. The KT63 has a piggy back lead that you place the earth lead into to test across L-N I am not truly sure of the purpose of this but there it is. Perhaps you could shed some light on that?
 
Of course there is PSCC and PEFC which I also understand before you go there. I know I should have said loop test. Or PFC PSC even
 
Last edited by a moderator:
Depending on circumstances, main earth may need to be disconnected to verify certain fault conditions..
All comes down to knowledge, understanding what is going on and being in control of the location.
 
Depending on circumstances, main earth may need to be disconnected to verify certain fault conditions..
All comes down to knowledge, understanding what is going on and being in control of the location.

What conditions would they be?
I can't think of any reason to have an installation which relies on ADS energised without its connection to the earthing system.
 
Of course there is PSCC and PEFC which I also understand before you go there. I know I should have said loop test. Or PFC PSC even

Yes it is a loop impedance test which is carried out.
PFC and PSC are not tested or measured, they are calculated by the meter based on the loop impedance and voltage measured at the time.
 
I have also disconnected the main earth to demonstrate to apprentices how parallel earths can appear to drag down the Ze or Zs readings of a TT installation.
I have also disconnected the main neutral to demonstrate how this can be dangerous..
 
Whatever the justification for energising some hypothetical system with the earth disconnected for demonstration or analytical purposes, the OP had a specific task in hand which was to trace a connection to a section of CPC that did not seem to start at the origin. As such, it's a simple continuity test to the MET, other CPCs or mass of earth, that does not require the system to be energised to trace. There is no justification here to work with the system energised.
 

Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net