Discuss Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net
What conditions would they be?
I can't think of any reason to have an installation which relies on ADS energised without its connection to the earthing system.
Ever been to a property that has an earth fault due to the neighbours or for other extraneous reasons?
As long as there are no members of the public, what have you, present, does it matter?I don't believe I have, but I don't see how that requires the installation to be energised without being connected to earth?
As long as there are no members of the public, what have you, present, does it matter?
How on earth would you risk assess it as safe to do to start with?
Ha - I start by safely isolating the supply, not the earth .The same way you would for any other earth fault that could potentially give you an electric shock.
Ha - I start by safely isolating the supply, not the earth .
Maybe, in my dreams .And if you can’t safely isolate the supply?
Do you check the earth before you touch the metal board?
Maybe, in my dreams .
I’d start a new thread if I were you and explain why you are doing this in the first place. Only disconnect the main earth to get a Ze reading. Then do dead tests to investigate anything.did you finally find the root cause of your problem ? if yes i would appreciate you share it. i have the same. w / wo main Earth wire connected i read same Zs 1.5 ohms. ( TT system) . thank you
I have a TT system ( earth not connected anywhere in any panel with neutral ) and the result i git for Zs was too good to be true . I understood that for a TT system you can not get less than 10 ohms but in my case was 1.5 ohms. I just tested w/o main earth connected to see result..like trying to understand the phenomenonI’d start a new thread if I were you and explain why you are doing this in the first place. Only disconnect the main earth to get a Ze reading. Then do dead tests to investigate anything.
A Zs test with the main earth disconnected should never happen.
I understand what you are asking - you are saying how can the earth path be this good.I have a TT system ( earth not connected anywhere in any panel with neutral ) and the result i git for Zs was too good to be true . I understood that for a TT system you can not get less than 10 ohms but in my case was 1.5 ohms. I just tested w/o main earth connected to see result..like trying to understand the phenomenon
. I understood that for a TT system you can not get less than 10 ohms but in my case was 1.5 ohms
Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net