Zs reading with main earth disconnected

Discuss Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
39
Morning, just checking a lighting circuit on a house, I have the main earth disconnected and still get a zs reading of 2.2 ohms. No evidence of an earth spike and bonding goes direct to henley block.

Any suggestions why this could happen??
 
I have also disconnected the main earth to demonstrate to apprentices how parallel earths can appear to drag down the Ze or Zs readings of a TT installation.
I have also disconnected the main neutral to demonstrate how this can be dangerous..
 
Whatever the justification for energising some hypothetical system with the earth disconnected for demonstration or analytical purposes, the OP had a specific task in hand which was to trace a connection to a section of CPC that did not seem to start at the origin. As such, it's a simple continuity test to the MET, other CPCs or mass of earth, that does not require the system to be energised to trace. There is no justification here to work with the system energised.
 
did you finally find the root cause of your problem ? if yes i would appreciate you share it. i have the same. w / wo main Earth wire connected i read same Zs 1.5 ohms. ( TT system) . thank you
I’d start a new thread if I were you and explain why you are doing this in the first place. Only disconnect the main earth to get a Ze reading. Then do dead tests to investigate anything.
A Zs test with the main earth disconnected should never happen.
 
I’d start a new thread if I were you and explain why you are doing this in the first place. Only disconnect the main earth to get a Ze reading. Then do dead tests to investigate anything.
A Zs test with the main earth disconnected should never happen.
I have a TT system ( earth not connected anywhere in any panel with neutral ) and the result i git for Zs was too good to be true . I understood that for a TT system you can not get less than 10 ohms but in my case was 1.5 ohms. I just tested w/o main earth connected to see result..like trying to understand the phenomenon
 
I have a TT system ( earth not connected anywhere in any panel with neutral ) and the result i git for Zs was too good to be true . I understood that for a TT system you can not get less than 10 ohms but in my case was 1.5 ohms. I just tested w/o main earth connected to see result..like trying to understand the phenomenon
I understand what you are asking - you are saying how can the earth path be this good.
It isn't impossible to get a TT Ze of 1.5 ohms, but I agree it's unlikely most of the time.

So to understand what's going on I'd measure the rod specifically by turning off, and disconnecting main earth and loop testing from Live to the wire going to the earth rod.
If you get a better Zs (when it's all back together) then it's usually down to bonded copper service pipes as they make quite good electrodes, and if one of them is connected to a house which isn't TT then there's actually a low resistance path back to the sub-station that way.
Obviously, this can't be relied on, so it's important to make sure the rod itself has a reasonable impedance.

I've had a Zs at the board of 0.4 ohms on a TT system before now (due to bonded services), but the rod was measuring over 400 ohms which I decided was too high so put a new one in.
 

Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock