Bonding should be, yes. What other kinds of parallel paths could there be, bearing in mind during testing anything not relevant to the testing should be disconnected?


You're saying you disconnect parallel paths apart from bonding while taking a measurement? Good luck with that outside of a 2 up 2 down!

A list of parallel paths is endless. Motor sat on a steel platform for example. Try disconnecting that while measuring Zs.

My point is, parallel paths come and go during the life of the install. The CPC is there to stay so why having a worst case scenario such a bad thing?

For example, man fits motor, motor vibrates, man fits anti vibration feet, parallel path lost, Zs increases. Disconnection time now not achieved.

I'm not saying it's better, just cannot understand some people's resistance to calculate.
 
You're saying you disconnect parallel paths apart from bonding while taking a measurement? Good luck with that outside of a 2 up 2 down!

A list of parallel paths is endless. Motor sat on a steel platform for example. Try disconnecting that while measuring Zs.

My point is, parallel paths come and go during the life of the install. The CPC is there to stay so why having a worst case scenario such a bad thing?

For example, man fits motor, motor vibrates, man fits anti vibration feet, parallel path lost, Zs increases. Disconnection time now not achieved.

I'm not saying it's better, just cannot understand some people's resistance to calculate.
The original question was about a college question, but if a Zs were likely to be increased the person likely to be increasing it should measure the Zs when he alters it.
Similar questions have come up before, and the general consensus is you can't account for alterations which may be made.
 
You're saying you disconnect parallel paths apart from bonding while taking a measurement? Good luck with that outside of a 2 up 2 down!

A list of parallel paths is endless. Motor sat on a steel platform for example. Try disconnecting that while measuring Zs.

My point is, parallel paths come and go during the life of the install. The CPC is there to stay so why having a worst case scenario such a bad thing?

For example, man fits motor, motor vibrates, man fits anti vibration feet, parallel path lost, Zs increases. Disconnection time now not achieved.

I'm not saying it's better, just cannot understand some people's resistance to calculate.

Why arse around calculating when you can directly test/measure the Zs at any given point on the circuit, and get an accurate value into the bargain!!!
 
Because it can be safer, but it seems we're going around in circles now.

Listen, ...if you can't safely undertake Ze/Zs tests or any other live testing, then there's something very wrong and shouldn't be in this industry. Live testing is a fundamental necessity for assessing electrical installations, end of!! I'm not going round in circles, i've stated previously i would not accept a calculated value, it's either a directly tested value or Nothing!!...
 
Listen, ...if you can't safely undertake Ze/Zs tests or any other live testing, then there's something very wrong and shouldn't be in this industry. Live testing is a fundamental necessity for assessing electrical installations, end of!! I'm not going round in circles, i've stated previously i would not accept a calculated value, it's either a directly tested value or Nothing!!...

Depends on the circumstances.
 
Listen, ...if you can't safely undertake Ze/Zs tests or any other live testing, then there's something very wrong and shouldn't be in this industry. Live testing is a fundamental necessity for assessing electrical installations, end of!! I'm not going round in circles, i've stated previously i would not accept a calculated value, it's either a directly tested value or Nothing!!...
Who said anything about Ze? Why would you not be able to take a live Ze reading? And how else would you take it?
 
Listen, ...if you can't safely undertake Ze/Zs tests or any other live testing, then there's something very wrong and shouldn't be in this industry.

There IS something very wrong with the industry unfortunately.

What if you were using metallic containment as the CPC?

Measure is the only solution.

Why arse around calculating when you can directly test/measure the Zs at any given point on the circuit, and get an accurate value into the bargain!!!

Because it can take hours to get ISO locks taken off and reinstated.

And you can get accurate results with a brew in your hand rather then an MFT.
 

Reply to zs testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
925
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
651
Hi Im an apprentice and just wanted to clarify domestic style wiring since i work industrial and don't deal with conventional wiring. in college...
Replies
1
Views
935
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
757

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock