Just a quick question , when carrying out zs test on a ring main in an office area , can you carry out this test whilst any appliance such a pcs are plugged into the circuit - i dont believe this is the case but just would like to confirm this.

Thanks
 
It's virtually impossible to switch off and unplug all pc's in an office location, so the answer if you've got no option you have to, did you experience any abnormal readings?
 
Hello Guys.
Just a quick question , when carrying out zs test on a ring main in an office area , can you carry out this test whilst any appliance such a pcs are plugged into the circuit - i dont believe this is the case but just would like to confirm this.

Thanks

It is not ideal, and i wouldn't do it because there is a remote chance that you could damage something, ok the chances are negligible, but if it something goes bang, then the cost could be a lot more than negligible.

My best advice would to be do the dead testing, you can do this with everything plugged in. So confirm ring continuity, do the r1+r2, (i would skip the r1+rn unless there is a pressing reason not to, as it is a periodic), then calculate your Zs, job done, and use test method 2 for the insulation resistance test. You could agree with your client to exclude this circuit, and record it as such under "Extent and Limitation", but it will need a test sooner or later.

Cheers…………Howard
 
but, Howard, if you're going to power down for dead tests, you may as well unplug all equipment anyway.
 
Are you physic Tel every time I am going to say something you beat me to it with the same answer, or is it merely a case of great minds.....
 

Reply to ZS Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
841
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
826
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
738

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock