OP
biospark80
Hi Iv'e spoken to Schnieder technical and they have come up with a a vigirex unit and toriods which are essentially a rcd unit with ct's. This shall give the additional protection required due to the high Zs.
Discuss Zs to high on MCCB Protected circuit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The op as not mentioned that but I have done a quick basic calc and I got a volt drop of around 30 volts at 100 amps, 550 meters seems way to long for this size of supply I am also interested to find out how the correct volt drop was achieved, You would need to go down to about 25 amps max load to get any were nearWhy are you trying to find solutions to this problem which obviously lies with the designer and installer of this cable ? what's your extent of involvement here ?
You say in your OP you are checking a cable, are you doing the initial verification ?
What horrible figure have you arrived at for volt drop ?
The op as not mentioned that but I have done a quick basic calc and I got a volt drop of around 30 volts at 100 amps, 550 meters seems way to long for this size of supply I am also interested to find out how the correct volt drop was achieved, You would need to go down to about 25 amps max load to get any were near
Yes I agree For 160 amp I think you would would be looking at 2x 300mm in parallel ( I'm only Guessing By the way) I think sorting the Zs is the least of his worries , I don't think any calcs have been done I thinks someone looks in regs on the table for cable size for swa seen that a 70mm will take 173 amp underground and said that will do it !!!I don't think it has been. It doesn't sound as if the calcs have been done correctly for this install which is why I brought the volt drop up, as the OP seemed only concerned about the high EFLI value and maybe hadn't considered VD in his solution.
Yes I agree For 160 amp I think you would would be looking at 2x 300mm in parallel ( I'm only Guessing By the way) I think sorting the Zs is the least of his worries , I don't think any calcs have been done I thinks someone looks in regs on the table for cable size for swa seen that a 70mm will take 173 amp underground and said that will do it !!!
It may be OK if its just a one light and a socket but I don't think that is going to be the case we will have to see if the OP comes back with any more info :willy_nilly:
Ok thanks for coming back to us and sorry for the miss understanding ,what was the calculated volt drop on it cable ? must of been close to the maxHi Guys some people are clearly not readings this thread from the start. To clear some details up,
Source - 160 3ph+n panel board.
MCCB- 50/35a settings max Zs 0.38 Ohms
Cable - 550mtrs of 4c 70mm Xlpe swa
Load - 3ph-n Db but only requires 35amps of load to be used.
The r1 + r2 value of the cable is 0.8 Ohms measured, which clearly shows that the Low Max Zs is not obtainable.
Schnieder has now come back to me and recommended a Vigirex unit with toroids. This kit will give me an adjustable range of protection from 0.3-1 amp earth leakage current on the cable which shall bring it inline with BS7671.
if the supply is 0.8 then surely the circuits coming off it wont comply
0.8ze for a distribution circuit is quite high with other circuits coming off it, maybe not now but in the future when they go to expand.Why is that?
0.8ze for a distribution circuit is quite high with other circuits coming off it, maybe not now but in the future when they go to expand.
just did a quick google search and 4c 70mm swa is £23m.
for 500m thats 11k surely it might have been a better design for another supply from the grid
but the OP said he was putting in an upfront rcd would that not cover the disconnection time for all final circuits aswell , saying that i don't think the design is the best but we don't know the resons for the design and there could well be a good reason fot it0.8ze for a distribution circuit is quite high with other circuits coming off it, maybe not now but in the future when they go to expand.
just did a quick google search and 4c 70mm swa is £23m.
for 500m thats 12.5k surely it might have been a better design for another supply from the grid.
especially if they only needed a 30amp supply
true but i cant see why the original installer did thisbut the OP said he was putting in an upfront rcd would that not cover the disconnection time for all final circuits aswell , saying that i don't think the design is the best but we don't know the resons for the design and there could well be a good reason fot it
true but i cant see why the original installer did this