Discuss zs unexpected results in the UK Electrical Forum area at ElectriciansForums.net

Testing a ring final ..ze = 0.22
.r1 + r2 =0.65...
R2 +rn = 0.69
So calculated zs = 0.87
But when I test at sockets they are around 1.47

Don't know what happened to my last post so here goes again, your r1+r2 result, is that the figure of eight result? ( R1+R2)
Losing it big time here the result of 1.47 ohms is that the average of all the sockets? or is it from one particular socket which could be a spur?
 
your R1+R2 should be (r1+r2)/4 i.e. approx 0.17. add that to 0.22 and you get Zs= 0.39.
 
Don't know what happened to my last post so here goes again, your r1+r2 result, is that the figure of eight result? ( R1+R2)
Losing it big time here the result of 1.47 ohms is that the average of all the sockets? or is it from one particular socket which could be a spur?

Yes to the figure of eight and yes it was the average sockets were reading between 1.43 and 1.5
 
Is the ring a new installation or old. Contacts on older ring socket outlets can fur up badly if not used which could lead to high readings. Take a couple of readings from back of socket and compare.
 
That is a little hard to understand Scott as, like the others have said, you've mixed up lower and upper case.

I find if anything when measured at sockets it can be 'less' then Ze + (R1+R2) due to Main bonding. Have you measured with a plug in tester? If so, it may be a good idea to use someones elses tester to see if you get the same results, or perhaps take the socket off and test actually on the conductors.
 
Last edited:
Testing Zs via a plug top lead can always give you false values even on new installs and why i rarely if ever use them. Test at the sockets terminals if you want accurate values that aren't relying on what is, just a scraping plug top connection..
 
I'm a bit suspicious of ALL the readings being the same. Are you sure you nuled the leads and had the tester on the correct setting?
 
Are you testing on the no trip setting on your meter? In practice this rarely gives accurate results....usually higher than the actual value. I had this discussion with Megger after I found that my meter gave wildly variable results on successive tests on the same point.Their reply was that accuracy isnt that important on the no trip setting as the RCD means much higher values are acceptable anyway!!. Renders the no trip setting a little pointless IMO.
 
Agree with Wirepuller re the no trip!

Also when using the No Trip 15mA setting you can with certain RCD's get unusually high ZS readings due to the internals of the device.

Alarmbells should start ringing if the results are not what you expect and a futher bit of investigation work is needed to see if there is a problem!

Bypass the RCD and ZS the circuit from the DB using the 25A high current ZS test if in doubt!
 
Agree with Wirepuller re the no trip!

Also when using the No Trip 15mA setting you can with certain RCD's get unusually high ZS readings due to the internals of the device.

Alarmbells should start ringing if the results are not what you expect and a futher bit of investigation work is needed to see if there is a problem!

Bypass the RCD and ZS the circuit from the DB using the 25A high current ZS test if in doubt!

This is going to start one of those debates....

It is exactly,what a competent tester could consider,as part of his investigation,but is frowned upon,by some assessors and instructors.

I reckon it is part of simplifying the instruction process,or one of a number of other reasons.

I have had this from trainers,and read this in many testing instructional books,but cannot see the difference between this "bypassing" and other bypass procedures,such as disconnecting bonding,for the purpose of a specific test.

One assessor i spoke to,concerning this anomaly,told me eventually "...well,bonding is one conductor,and one terminal..." and that bypassing any RCD,was "more involved..."

...Maybe it's just the same feeling of frustration,older dudes have,on finding some grads dissertation got a 1:1,with a spelling mistake on every other line,"coz,the content trumped it..." :icon12:
 
This is going to start one of those debates....

It is exactly,what a competent tester could consider,as part of his investigation,but is frowned upon,by some assessors and instructors.

I reckon it is part of simplifying the instruction process,or one of a number of other reasons.

I have had this from trainers,and read this in many testing instructional books,but cannot see the difference between this "bypassing" and other bypass procedures,such as disconnecting bonding,for the purpose of a specific test.

One assessor i spoke to,concerning this anomaly,told me eventually "...well,bonding is one conductor,and one terminal..." and that bypassing any RCD,was "more involved..."

...Maybe it's just the same feeling of frustration,older dudes have,on finding some grads dissertation got a 1:1,with a spelling mistake on every other line,"coz,the content trumped it..." :icon12:

I wonder if the OP had done an R1 + R2 on another circuit on the same RCD, and then done a Zs, to see if the higher reading was consistent?
 

Reply to zs unexpected results in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock