Zs

Discuss Zs in the Industrial Electricians' Talk area at ElectriciansForums.net

Hi Ringer,

Cheers for your feed back, the actual question says, Explain , briefly the most likely reason why the actual test result (0.51) would normally be less then the value calculated (which i we worked out to be 1.09 )

Does a dead test R1+R2 reading (measured have parrell paths which might make the reading lower?

Regards

Locket


Parallel paths..

next question?
 
If the ambient temp at the time of the reading is less than 20C then that may be another reason for the actual being less than the calculated value. Though with the actual being roughly half of the calculated, suspect there may be another reason. Don't have enough practical testing experience myself to be able to answer this any better.
 
Hi Widdler,
Itake it you think its parrell paths when you do adead test R1+R2 reading with the low ohm meter, it was just a guess as i thought you only got parrell paths when you did the Zs measured reading with the loop imp metre?

Kind Regards

Locket
 
If the question was describe 'briefly' why, then yes, parallel paths would seem to be the answer. But what sort of parallel paths would you find in a lighting circuit when doing R1+R2, because you have disconnected from the MET, unless it is referring to the commoned cpc at all points within that circuit?
 
When we do R1+R2 test at college we use a crocodile clip attaching say the appropriate line cable connected with the clip on one end to the cpc busbar (not disconnected appriopriate cpc) but even then where would the parrell paths be even doing it this way ,i dont understand.

locket
 
ah just re-read and seen workshop lighting mentioned - could this mean it is in steel conduit and that is your parallel path? Also can't remember was it in singles which would also make you think conduit.
 
Hi Pushrod,
Ithink you might have nailed it, sorry i havnt given the full drawn scenario , but it does say in the workshops the single cables are run in surface mounted steel conduit and trunking, so bearing this in mind ,my question to you is,when doing a dead test R1+R2 with the standard low ohm meter, would you still get parrell paths effecting the reading as you think above giving you a lower reading?

Regards
 
Many thanks Pushrod,

ive loads more questions for you as im only a novice but ill start with them another night as i think ive tested you enough tonight and my head is now hurting,

Many Thanks Sincerely

LOcket
 
If I may but in...

To find out if the students can do it the question asked the R1+R2 to be calculated from the length and resistance of the cable. That's understandable as is asking why the calculated value may be higher than the measured.

However, I am a bit confused as to why the measured R1+R2 of 0.51Ω is mentioned at all. The fact that it is so low, comparatively, seems to be confusing everyone but, surely, it is irrelevant and could have been given any value or is there something we don't know - another part of the question?

edit - I may have taken too long typing this.
 
Last edited by a moderator:
Hi Pushrod,

I see what your thinking but its on an old 2391 test paper,it gives you a Sched of Test Result sheet with a lighting circuit of 45 n long and an R1 +R2 reding of 0.52 , which must be the dead test reading. The Q. asks you to calculate the maximum expected test result value for the info given in a table showing 1.5 mm cable ,with 12.1 mohms/m value at ambient temp of 20 degrees.

To me its just asking for a like for like value of R1 +R2 cold , not any 1.2 con oper temps etc, so why should the dead test reading be more then the calc value , im confused

Regards

Locket

hi mate the measured value will include parallel paths the calculated is a more accurate value and does not include parallel earth paths
ie your conduit and the main protective bonding conductors will introduce parallel paths so not a accurate measurment
 
Last edited:
Hi Pushrod,
Ithink you might have nailed it, sorry i havnt given the full drawn scenario , but it does say in the workshops the single cables are run in surface mounted steel conduit and trunking, so bearing this in mind ,my question to you is,when doing a dead test R1+R2 with the standard low ohm meter, would you still get parrell paths effecting the reading as you think above giving you a lower reading?

Regards

This would have been answered much sooner with this info.
 
When we do R1+R2 test at college we use a crocodile clip attaching say the appropriate line cable connected with the clip on one end to the cpc busbar (not disconnected appriopriate cpc) but even then where would the parrell paths be even doing it this way ,i dont understand.

locket

Have you asked your tutor why?

Just think about it. by clipping direct onto the earth bar you are connecting to all the other CPC's on that board. If that Earth bar is the installations MET, then you will also have the bonding conductors to the services, may not be gas but certainly water, that will also be on there, so you have all those parallel paths.
 
Many thanks Malcolmsfield,

If doing R1+R2 test as i said i do at college and it also shows you to do in O.S.G ,G.N.3 etc , this then obviously decreases the resistance due to parrallel paths etc as you explained , which then asks me the question is this then the true R1 +R2 reading?,
and so with or without earthed steel conduit as you said , there would still be parrallel paths.

Kind Regards

Locket
 

Reply to Zs in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
484
Hi All, Any help would be greatly appreciated. When calculating the Zs for a circuit specifically for 2396 do you have to incorporate the on site...
Replies
0
Views
484
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock