Discuss Zs in the Australia area at ElectriciansForums.net

K

kduck

Hi,

what is Zs I no it is the earth fault loop impedance, but what are we measuring.
 
Last edited by a moderator:
It is the path that faults would take from the phase of the supply transformer to the installation location,thro the circuit to the fault, down the cpc to the installation main earth terminal and back to the earthed star point of the supply transformer

Therefore ZS = ZE+R1+R2

ZS is the measurement of the Whole of the fault path
ZE is the measurement of the external section
R1+R2 measurement of the circuit of the installation

The Zs then has to be low enough to allow sufficient current to flow in order for the protective device to operate in the required time
 
It is the path that faults would take from the phase of the supply transformer to the installation location,thro the circuit to the fault, down the cpc to the installation main earth terminal and back to the earthed star point of the supply transformer

Therefore ZS = ZE+R1+R2

ZS is the measurement of the Whole of the fault path
ZE is the measurement of the external section
R1+R2 measurement of the circuit of the installation

The Zs then has to be low enough to allow sufficient current to flow in order for the protective device to operate in the required time

Zs = Ze + (R1 + R2)
 

Reply to Zs in the Australia area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
528
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
481
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Still having a discussion @ work about this…TNCS system DB/CU is a split 30ma RCD configuration,5/5 MCB’S are 60898 what Max Zs would you put in...
Replies
31
Views
1K
What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
Replies
7
Views
658

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock