Recent content by Rkidcd

  1. R

    VIGI module test

    ??
  2. R

    VIGI module test

    thanks, you encouraged me to research hi current test currents for megger MFT’s. Turns out they can put out up to 20A so there is a risk unless I ramp the VIGI up to 30A for the duration of the test.
  3. R

    VIGI module test

    What’s the chances of tripping this VIGI module set @ 10A when performing downstream no trip high current Zs tests.
  4. F4D18B53-343D-4A81-AEC4-A7067E747F74.jpeg

    F4D18B53-343D-4A81-AEC4-A7067E747F74.jpeg

  5. R

    Strange RCD tripping scenario

    Initial verified them all yes - not since tripping though as only happened this afternoon - gonna have to delve into it tomorrow
  6. R

    Strange RCD tripping scenario

    It could be something as simple as this Tony
  7. R

    Strange RCD tripping scenario

    All final circuits tested as stated
  8. R

    Strange RCD tripping scenario

    I’ve thought about trying a 300mA - there’s over 20 Rcbo’s I haven’t ramp tested but I have had 2 different manufactured RCD’s in today, both tripping
  9. R

    Strange RCD tripping scenario

    I haven’t but sounds like it could be a good purchase
  10. R

    Strange RCD tripping scenario

    Thanks, most of the above makes sense to be honest - you do in fact get away with it on TT majority of time in like you say. However why doesn’t the RCBO trip ahead of the time delayed?
  11. R

    Strange RCD tripping scenario

    Any suggestions as to possible causes of RCD tripping in the below domestic scenario would be helpful: Origin: single phase TT supply into an external cabinet housing cutout and our installed 100A 100mA Type S 2Pole RCD. Earth Rod has also been sunk here. House: 3c SWA supply to house from...
  12. R

    PME METAL OUTBUILDING

    Gonna potentially be flamingos and other similar birds - lighting would be within a 2m height of the solid ground/water sections. IP rated a must? ELV recommended?
  13. R

    PME METAL OUTBUILDING

    No involvement to date, just looking into the feasibility of installing circuits from this extremely poorly designed DB/supply
  14. R

    PME METAL OUTBUILDING

    Another quick question about the same job but completely different subject. How would you go about zones in the following scenario: A wildlife hut which is semi open to the elements. Half of hut is solid ground the other half vaguely described as a pool, pond or collection of water (through...
  15. R

    PME METAL OUTBUILDING

    Thanks for the reply. Things have developed further since this morning - when I took a Zs at the DB with the supplementary Rod connection disconnected leaving me just PME I achieved a Zs of well over 2 ohms on a B63 MCB with no associated RCD!! Am I right in saying if I isolate the source...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock