Discuss VIGI module test in the UK Electrical Forum area at ElectriciansForums.net

Rkidcd

-
Reaction score
2
What’s the chances of tripping this VIGI module set @ 10A when performing downstream no trip high current Zs tests.
F4D18B53-343D-4A81-AEC4-A7067E747F74.jpeg
 
Last edited by a moderator:
Depends on what current your tester puts out my old Robin puts out a 25A pulse. These are handy for testing I usually bump them up to maximum but if it is there for specific protection then this maybe unwise unless that protection isn't relevant whilst you are undertaking the test
 
Depends on what current your tester puts out my old Robin puts out a 25A pulse. These are handy for testing I usually bump them up to maximum but if it is there for specific protection then this maybe unwise unless that protection isn't relevant whilst you are undertaking the test
thanks, you encouraged me to research hi current test currents for megger MFT’s. Turns out they can put out up to 20A so there is a risk unless I ramp the VIGI up to 30A for the duration of the test.
 
thanks, you encouraged me to research hi current test currents for megger MFT’s. Turns out they can put out up to 20A so there is a risk unless I ramp the VIGI up to 30A for the duration of the test.
Not necessarily as you can up the t(ms) to maximum.
 

Reply to VIGI module test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

can every single car module cause a short circuit? my test light stays on between batt and terminal unless i unplug every single module? any advice?
Replies
20
Views
2K
Hello everyone, I recently want to purchase some IBC photovoltaic modules for testing. However, since there are currently not many providers of...
Replies
0
Views
542
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
219
Just wondering if someone could help provide an explanation as to why this might be the case when testing an RCBO. Testing the RCBO at the DB...
Replies
7
Views
273
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
440

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock