Andy Barton
hi I'm a part qualified electrician gaining exp wherever I can whilst doing my college course.
Today we were hooking up a static caravan with 3 core swa. All was good until we started doing the tests. With the pme connected I was getting 0.26 as an earth loop at the board in the van. The boss then told us it really needed to be put on a tt so I duly banged in a stake and connected it all up. Now when tested is was getting just over 21 in my loop so I can't understand why this is better than using the pme.
I asked the question but neither the boss or the spark could really answer me. To add to my confusion I was also told to remove the core I had been using in the pme system to the met in the mobile home. I would have imagined belt and braces would be to have both earths connected the tt and the pme?
If somebody in the know could give me an answer on this it would be appreciated.
Thanks in advance
Today we were hooking up a static caravan with 3 core swa. All was good until we started doing the tests. With the pme connected I was getting 0.26 as an earth loop at the board in the van. The boss then told us it really needed to be put on a tt so I duly banged in a stake and connected it all up. Now when tested is was getting just over 21 in my loop so I can't understand why this is better than using the pme.