acceptable

  1. N

    Is this acceptable?

    Hi Everyone. Im a first year apprentice and would like some opinions please. I know that lighting is normally wired in 1.5mm and sockets wired in 2.5mm. However, our shed at home has a 1.5mm SWA wired to our small shed for a light. Would one double or even single socket be able to be wired...
  2. M

    Is this acceptable, apparantly yes??

    Ive been speaking to a spark who has said that on doing kitchen part rewires every day for b an q that you can use a maintenance free connection unit and then bury the cables in the wall, i.e plaster over them, save lifting boards upstairs, is this the case now, sounds bit rough to...
  3. P

    Acceptable spur length from fcu

    Putting a final ring in kitchen and will have a fcu on the ring for the cooker hood. I want to then run from fcu up wall to a flex plate. Due a window above the fcu I can't run straight up and it also wouldn't be where the outlet needs to be. I can run down from the fcu, under the floor...
  4. S

    Perfect PIR

    Just wondering if anyone has ever come across a perfect PIR? Nearly had one today, but a busbar point without a rubber topping stopped it. All tests where fine though, and that and no rubber gromits in some back boxes. So not a major deal.
  5. V

    testing calc question

    a 10amp type c has a max measured zs of 1.85,i have a circuit with a measured zs of 2.03 the circuit is 2.5mm (not sure type) and it provides roof lighting also r1+r2 was 2.77ohms. is there any way i can make the zs result acceptable using the design zs from the regs or does this circuit just...
  6. S

    2.5mm and 4mm in same ring - acceptable?

    As per the title. And if so, what would you put on the schedule of test results? (One end of the ring is 2.5mm and the other 4mm - so it is obvious at the CCU). I am assuming it is 4mm. It is old colours (black and red) and the conductors are stranded so I'm thinking it's not 2.5mm. The...
  7. U

    Is this acceptable

    An electrician had to install a new electrical supply to air conditioning condensors and internal cassette 2 no 30 A supplies 1 no 10 A supply to internal unit Instead of running these from the incoming mains board they did the following They installed a new consumer unit along side an...
  8. T

    Acceptable means of making a spare live conductor safe - inside external floodlight

    I've got an old floodlight outside my domestic property that I want to replace with a new Low-Energy unit. The new unit has no PIR, so just has a Live, Neutral & Earth connector inside the IP65-rated housing. The connector itself has push-buttons cable clamps a bit like cheap speakers have, so...
  9. sythai

    Is this acceptable....? (got my doubts)

    Domestic property with extension, 1 x cu supplying extension and exisiting cu supplying house... both fed from same single phase cut out. 2 way lighting between extension an existing house, and at one of the 4 gang switches there are 2 different circuits in there one from extension cu and one...
  10. P

    is this acceptable??

    i'm not a domestic spark or a plumber for that matter, but my da phoned the other day to say my granny had no hot water function from her boiler, dual programmer and the heating was working fine. traced the fault to a two port motorised valve with aux. contacts not working and to pull her out of...
  11. E

    Is 0ne 30mA RCD acceptable to cover all circuits in 3 bed semi - any reccomendations

    Hi , Im looking at doing a rewire on a small 3-bed semi. Im pretty much upon the current regs e.t.c. and am aware of the need to prevent complete loss of lighting (i.e upstairs and downstairs) in the event of an RCD tripping e.t.c However as apparantly there is a need to protect all cabling...
  12. J

    think ive just stuffed my am2

    On the m.i.c.c cable the 3 phase from the board the resistance between each phase is about 88 mega ohms so think ill get marked dorwn for that also the in the board the conducters are about an inch short of the breaker the only thing im pleased with is the conduit oh well got another 2 days of...
  13. T

    1.5mm SWA, Acceptable or bad practice ?

    I know it depends on its inststallation method but what is the max current carrying capacity of 1.5mm swa 3 core? If im looking at the correct table 4D4A it says 18a clipped direct. But then this manufactures spec says 32a. (page 3) http://www.alertelectrical.com/upload/pdf/329armoured.pdf...
  14. S

    Acceptable Ze value for a TT System

    Hi All Hope you are having a good day. What is an acceptable Ze value for a TT system?? I know TNCS = 0.35 and TNS = 0.8. Cheers Dan
  15. S

    acceptable zs

    Hi all , trying to get ready for elecsa assesment. planing to show new cu insall on my own home 17th ed of course. Problem is that TTearthing :eek: put in 1 rod got reading of aprox 230 ohms zs(very rocky stoney ground) on socket outlets so put in anoter linked to the first now geting a reading...
  16. B

    Is this acceptable practice?

    Opened an old wylex cu today and there was a 10m cable feeding stand alone breaker for shower fed from live side of main switch together with 25m/m tails is this acceptable practice? myself I would of split the tails.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock