Is it safe to use single pole RCBOs on a TT earthing system without an rcd and just a double pole breaker?
What would the max allowable earth resistance be to cut out a earth to neutral fault?
Hi all,
Is anyone interested in the following list before it goes on Ebay? All brand new, left over from previous jobs:
1 x MR30 Pod
1 x Aico Ei261 Carbon Monoxide
3 x Aico Ei100MRF Radio Module
1 x Aico Ei3016 Smoke
9 x Square D iKQ SE10C325 TP MCB's 25amp Type C
2 x Merlin A9D11816 RCBO 16a...
Hello
Is it OK to use a 32 amp rcbo on a radial Circuit. Cable size is 6mm2, cable length is about 15 m. There are 4 double plugs on the circuit. Loads are kettle 2.2 kw, washing machine max 2 kw, electric cooker 1 kw.
Cheers
Is it acceptable, using a two-wire RCBO tester, to test at a light switch using the phase and earth wires?
If it is acceptable are there any disadvantages?
Evening all,
I changed a board today in a ground floor flat. 3 circuits with separate RCBOs (Shower 40A, sockets 32A, and Lights 6A)
Switching on any light switch causes the both RCBOs for the lights and sockets to trip.
Insulation resistance results are in the 100s between conductors on...
Hi,
Can anyone please explain why my friend's 30mA trip RCBOs passes the trip test (e.g. x5 is less than 40ms) when the test is done at the consumer unit but fails when the test is done at the sockets.
Is he doing something wrong or is there a fault somewhere (the RCBO or the circuit...
Hello everyone,
I have a garage full of electrical gear as i'm sure many of you do, various bits left over from jobs. Part on my lifelong mission is to keep getting bits out and not just getting gear in, as it's all money!
So i literally have thousands of old MCB's, RCD's, RCBO's fuses...
I was always taught never to trim RCBO leads. I noticed on another thread the other day/earlier on that someone said they did.
What’s the general consensus on the subject? The reasons explained to me as to why we shouldn’t cut them were the RCBO was calibrated with that length of cable on so it...
Has anyone installed the new compact rcbo from crabtree and noticed a flaw that they have introduced that doesn't exist on the older larger model starbreaker rcbo..
The basics of it are that the new compact rcbo when plugged into the busbar in a circumstance that many will come across where you...
recently brought a new Wylex RCBOb NHXSS1B16
It has not come with a earth tail like all the older NHXSBS1B16 but had the neutral tail.
Do I just connect the earth from the cable I’m feeding into the earth bar ?
Just curious tbh ....
Hi,
A relative has moved into a flat with a mid-80's Square D QO1 12F distribution board, which has MCBs on all outgoing ways.
There are proposals to update the kitchen with a desire for some additional socket outlets. To meet the requirements of Part P and by extension, BS 7671, RCD protection...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.