Discuss 110 V Motor Question in the UK Electrical Forum area at ElectriciansForums.net

Blackpool

DIY
Reaction score
2
Hello everyone, I have a piece of 110V plant that is not working. The wire from plug to NVR had a partial cut (rectified). The NVR energises so assumed good. The motor has what looks like two capacitors (white and black). I am trying to run some basic checks on the windings (resistance) but wondered if the capacitors could corrupt the readings. I completely disconnected one (the black one) and I am showing low resistance on all fields. Could the white one be causing that? Or is the motor faulty? Could it be repaired? Image attached.
 

Attachments

  • Image.png
    1.1 MB · Views: 29
It's a little hard to follow exactly what you have there. It is likely to be a capacitor start and run motor, in which the main winding is connected directly to the supply, the auxiliary winding is connected via the run (smaller value) capacitor, and the start (larger value) capacitor is paralleled to the run cap in series with a centrifugal switch that opens when the motor reaches speed.

If the capacitors are OK (and not shorted) then you should see two or three separate circuits through the leads emerging from the motor frame - the main winding, the aux winding and the centrifugal switch. The coils might be a few ohms, the switch a fraction of an ohm. There might also be a thermal cutout in series with both windings.

Capacitors are the least reliable part of the motor. A shorted cap can kill the winding, an open cap might just prevent starting. What actually happens when energised now? Does it hum? Will it start if rotated manually?
 
It's a little hard to follow exactly what you have there. It is likely to be a capacitor start and run motor, in which the main winding is connected directly to the supply, the auxiliary winding is connected via the run (smaller value) capacitor, and the start (larger value) capacitor is paralleled to the run cap in series with a centrifugal switch that opens when the motor reaches speed.

If the capacitors are OK (and not shorted) then you should see two or three separate circuits through the leads emerging from the motor frame - the main winding, the aux winding and the centrifugal switch. The coils might be a few ohms, the switch a fraction of an ohm. There might also be a thermal cutout in series with both windings.

Capacitors are the least reliable part of the motor. A shorted cap can kill the winding, an open cap might just prevent starting. What actually happens when energised now? Does it hum? Will it start if rotated manually
It's a little hard to follow exactly what you have there. It is likely to be a capacitor start and run motor, in which the main winding is connected directly to the supply, the auxiliary winding is connected via the run (smaller value) capacitor, and the start (larger value) capacitor is paralleled to the run cap in series with a centrifugal switch that opens when the motor reaches speed.

If the capacitors are OK (and not shorted) then you should see two or three separate circuits through the leads emerging from the motor frame - the main winding, the aux winding and the centrifugal switch. The coils might be a few ohms, the switch a fraction of an ohm. There might also be a thermal cutout in series with both windings.

Capacitors are the least reliable part of the motor. A shorted cap can kill the winding, an open cap might just prevent starting. What actually happens when energised now? Does it hum? Will it start if rotated manually?

It's a little hard to follow exactly what you have there. It is likely to be a capacitor start and run motor, in which the main winding is connected directly to the supply, the auxiliary winding is connected via the run (smaller value) capacitor, and the start (larger value) capacitor is paralleled to the run cap in series with a centrifugal switch that opens when the motor reaches speed.

If the capacitors are OK (and not shorted) then you should see two or three separate circuits through the leads emerging from the motor frame - the main winding, the aux winding and the centrifugal switch. The coils might be a few ohms, the switch a fraction of an ohm. There might also be a thermal cutout in series with both windings.

Capacitors are the least reliable part of the motor. A shorted cap can kill the winding, an open cap might just prevent starting. What actually happens when energised now? Does it hum? Will it start if rotated manually?

Hello Lucien

Nothing happens. No start and no humming. The problem must be the switch, capacitors or motor.

Switch energises. No wiring diagram as yet for motor (plant manufacturer is trying to get one) so only basis tests run. By way of explanation, if i take the cover off the motor electrics (as seen in photo) and probe the three terminals (closest to black capacitor) i get 'a voltage' symbol on my test probe (so some power is passing through switch) albeit i cannot confirm precise amount. All three terminals behave that way (power indicated to all of them) BUT if i switch off and try again, invariably NO power to any of them. Switch off and then try again, power to terminals restored. Sometimes this intermittent power 'restored' happens on the next power on cycle, on other occasions its the third switch on.

So not sure if the protection in the switch Kedu JD3 is interrupting power and the second or third attempt is resetting it ... albeit the JD3 its clearly letting power through the switch (not instantly cutting it) so any need to reset seems 'after the event'. But in any event, motor never turns
 
Last edited:
Hello Lucien

Nothing happens. No start and no humming. The problem must be the switch, capacitors or motor.

Switch energises. No wiring diagram as yet for motor (plant manufacturer is trying to get one) so only basis tests run. By way of explanation, if i take the cover off the motor electrics (as seen in photo) and probe the three terminals (closest to black capacitor) i get 'a voltage' symbol on my test probe (so some power is passing through switch) albeit i cannot confirm precise amount. All three terminals behave that way (power indicated to all of them) BUT if i switch off and try again, invariably NO power to any of them. Switch off and then try again, power to terminals restored. Sometimes this intermittent power 'restored' happens on the next power on cycle, on other occasions its the third switch on.

So not sure if the protection in the switch Kedu JD3 is interrupting power and the second or third attempt is resetting it ... albeit the JD3 its clearly letting power through the switch (not instantly cutting it) so any need to reset seems 'after the event'. But in any event, motor never turns


Just checked the capacitors. The white one is on spec 80 microfarads (spec 80 microfarads) but the black one is 184-187 microfarads which is outside the stated parameters 145-174 microfarads
 
Start capacitors can have wide tolerance, that difference in value should not be a problem. Faulty caps are usually either open circuit or short circuit. The fact your motor does nothing points elsewhere. I'll reply in full later if I can
 
I see what looks like a 5-core cable entering the motor - brown/black/grey/blue/earth. Obviously this is more conductors than needed simply to operate a motor in one direction and speed, so:
  • Please can you confirm there is no other control functionality from the control box?
  • Can you confirm the functions of the cores at the other end, so that we know where to expect continuity at the motor end?
  • Can you post a pic and/or a sketch that clearly shows the connections to both capacitors?

With this info, we should then be able to make reasonable inferences about what resistances to expect across which motor terminals. It may be that the NVR coil is energised through a thermal cutout in the motor which would explain at least the 4th core of the cable.
 
Thanks Lucien. I believe the manufacturer of this plant just buys components, namely (1) switch assembly and harness and (2) complete motor from china and just swaps either out if a test rig indicates a fault on either.

Manufacturer has requested wiring diagrams from supplier. I chased them on Friday and not received yet. So will not have any definitive answers on cable and cores until then. Unless I can get the plastic fan off and have a look inside (see last paragraph below).

Will take a photo of capacitor connections tomorrow.

Just done some more testing and thinking. I am wondering whether the power to the terminals issue (mentioned in an earlier post) is actually a delay caused by the black start capacitor charging up. So to test this I hit the start button from cold (not touched for 24 hours and capacitors 100% discharged from testing and then reassembly) and the terminals did not get power for about 5 seconds. When I switched off and pressed start quickly, there was still power to terminals (presumably because start capacitor not having an opportunity to naturally dissipate its charge). But if i wait 5 seconds between switching on again, no power to terminals. So it looks like start capacitor takes 5 seconds to charge and 5 seconds to dissipate its charge when powered off.

Should there be instant power to those terminals? 5 seconds seems a long time for the plant to even think about powering up.

Regards the centrifugal switch. Not been able to take plastic fan off yet to gain access to have a look. I did try powering on and then manually spinning fan to help start (and try to engage run capacitor but nothing). Will have another attempt at gaining access tomorrow and also take photos of anything inside.
 
Last edited:
I am wondering whether the power to the terminals issue (mentioned in an earlier post) is actually a delay caused by the black start capacitor charging up.

The capacitors charge and discharge 100 times per second (on 50Hz AC). Some residual charge might be left on a disconnected capacitor but when the motor is functioning normally, no capacitor will be left open-circuited at rest.

We don't need to play guessing games. We just need to trace systematically from the NVR through the 5-core so we know which terminal is which in the motor.
 
Start capacitors can have wide tolerance, that difference in value should not be a problem. Faulty caps are usually either open circuit or short circuit. The fact your motor does nothing points elsewhere. I'll reply in full later if I can

The capacitors charge and discharge 100 times per second (on 50Hz AC). Some residual charge might be left on a disconnected capacitor but when the motor is functioning normally, no capacitor will be left open-circuited at rest.

We don't need to play guessing games. We just need to trace systematically from the NVR through the 5-core so we know which terminal is which in the motor.
The capacitors charge and discharge 100 times per second (on 50Hz AC). Some residual charge might be left on a disconnected capacitor but when the motor is functioning normally, no capacitor will be left open-circuited at rest.

We don't need to play guessing games. We just need to trace systematically from the NVR through the 5-core so we know which terminal is which in the motor.


I have attached some more images
 

Attachments

  • Another NVR Image.png
    1.4 MB · Views: 12
  • Black_connections.png
    1.6 MB · Views: 10
  • NVR Input.png
    1.3 MB · Views: 11
  • NVR Output.png
    941 KB · Views: 11
  • White_connections.png
    1.7 MB · Views: 12
OK right, so the cable from the NVR seems to be 4-core. If we number the three white terminals in a row 1 - 3 we have:
1 - brown switched line from NVR > two blacks into motor
2 - grey switched neutral from NVR > white into motor
3 - black switched line back to NVR hold coil via thermal protector > thin blue into motor

So the first circuit that we should see is zero ohms between 1 & 3 to enable the NVR coil to operate.
Then, we should see the motor main winding between 1 & 2.
The auxiliary winding and switch we have to measure by breaking into the capacitor leads but if there's nothing happening then we begin with the main winding.

What are the resistances 1-2, 1-3?
 
OK right, so the cable from the NVR seems to be 4-core. If we number the three white terminals in a row 1 - 3 we have:
1 - brown switched line from NVR > two blacks into motor
2 - grey switched neutral from NVR > white into motor
3 - black switched line back to NVR hold coil via thermal protector > thin blue into motor

So the first circuit that we should see is zero ohms between 1 & 3 to enable the NVR coil to operate.
Then, we should see the motor main winding between 1 & 2.
The auxiliary winding and switch we have to measure by breaking into the capacitor leads but if there's nothing happening then we begin with the main winding.

What are the resistances 1-2, 1-3?

Terminal screw heads were not reliable (no clean contact - dust, age corrosion etc) so to establish the correct reading I cleaned the crimped brass end fittings on each wire with wire wool and then reinserted into terminal block. Then touched the respective ends with thin gold plated probes.

1-2 = 0.3 Ohms (initially fluctuated between 0.3, 0.4 and 0.5 Ohms - settled quickly at 0.3)
1-3 = 0.0 Ohms
 
Well then something should be happening.

  • There is solid zero-ohm continuity from 1-3 through the thermal protector so the NVR coil circuit is complete and should hold on (does it?)
  • There is continuity of a fraction of an ohm through at least the main winding from 1-2 so the motor should hum or try to do something, even if it doesn't start normally.

We need to either prove that there is no power reaching the main winding, or that it is indeed getting power and any failure to start is localised to the auxiliary winding, centrifugal switch and/or capacitors. Latch on the NVR or hold the start button in by hand and check for the presence of 230V between 1- brown and 2- grey. Beware the possibility of the motor starting unexpectedly if an intermittent connection is disturbed.

If there is no 230V there, something is still amiss with the NVR connections. In theory, safety issues aside, it should be possible to make the motor operate independently of the NVR by disconnecting the incoming brown/grey/black cable from the white terminal blocks and connecting the mains supply directly L to 1 and N to 2 in place of brown and grey.

Out of interest, what exactly is this machine?
 
Well then something should be happening.

  • There is solid zero-ohm continuity from 1-3 through the thermal protector so the NVR coil circuit is complete and should hold on (does it?)
  • There is continuity of a fraction of an ohm through at least the main winding from 1-2 so the motor should hum or try to do something, even if it doesn't start normally.

We need to either prove that there is no power reaching the main winding, or that it is indeed getting power and any failure to start is localised to the auxiliary winding, centrifugal switch and/or capacitors. Latch on the NVR or hold the start button in by hand and check for the presence of 230V between 1- brown and 2- grey. Beware the possibility of the motor starting unexpectedly if an intermittent connection is disturbed.

If there is no 230V there, something is still amiss with the NVR connections. In theory, safety issues aside, it should be possible to make the motor operate independently of the NVR by disconnecting the incoming brown/grey/black cable from the white terminal blocks and connecting the mains supply directly L to 1 and N to 2 in place of brown and grey.

Out of interest, what exactly is this machine?

Yes the NVR energises and holds. But no hum or any movement.

The plant is a plate compactor (wacker plate). Albeit it is 110V (for on site safety - UK law) not 230V - so uses an external transformer (plugged directly into main domestic circuit so no extension cord voltage drops). Distance from domestic supply is 1m to transformer (using 3.3kva transformer's own inbuilt cable) and then used plant's own 1m harness cable to NVR. Transformer is brand new and rated to handle plant continuously (and tested on other plant).

Will check the voltage between 1 and 2 and then try the by-pass you suggested and revert back to you.

Manufacturer said they would be surprised if it was the motor (they are reliable) and suggested either NVR switch or capacitors as their initial thoughts. Manufacturer also confirmed fan can be removed with a couple of pry bars to gain access to centrifugal switch.
 
Yes the NVR energises and holds. But no hum or any movement.

The plant is a plate compactor (wacker plate). Albeit it is 110V (for on site safety - UK law) not 230V - so uses an external transformer (plugged directly into main domestic circuit so no extension cord voltage drops). Distance from domestic supply is 1m to transformer (using 3.3kva transformer's own inbuilt cable) and then used plant's own 1m harness cable to NVR. Transformer is brand new and rated to handle plant continuously (and tested on other plant).

Will check the voltage between 1 and 2 and then try the by-pass you suggested and revert back to you.

Manufacturer said they would be surprised if it was the motor (they are reliable) and suggested either NVR switch or capacitors as their initial thoughts. Manufacturer also confirmed fan can be removed with a couple of pry bars to gain access to centrifugal switch.


No power is reaching the terminal block. Which is odd because the other day there was some voltage.

Results :

104V into NVR (at +ve and -ve terminals on input side)
104V out of NVR (at +ve and -ve terminals on output side)
But nothing reaches the terminal block.
No damage in NVR to terminal block harness.

My original thought was the cut in between the plug and NVR may have shorted or blown something in the NVR?

I ran the bypass (basically severing the plug to NVR harness where the cut was ... leaving the earth still running to NVR and wired +ve and -ve into the terminal block and the motor fires up.

Is the issue likely to be the NVR contactor?
Do I still need to check the auxiliary winding and centrifugul switch?
 
104V out of NVR (at +ve and -ve terminals on output side)
But nothing reaches the terminal block.
Could there even be a break in the 4-core cable?
 
Could there even be a break in the 4-core cable?
That run of cable looks perfect. Its only just over 2 feet long and it securely clipped to the frame every 7 inches. So no real opportunity to break

I will test by checking the continuity of each wire from NVR output to terminal block.

I have a volt stick that glows when it detects power along a cable (and stops when there is a break) but it does not work on 110V
 
That run of cable looks perfect. Its only just over 2 feet long and it securely clipped to the frame every 7 inches. So no real opportunity to break

I will test by checking the continuity of each wire from NVR output to terminal block.

I have a volt stick that glows when it detects power along a cable (and stops when there is a break) but it does not work on 110V


I think you may have cracked the case Lucien !

Continuity across each pair of terminals on NVR when I press the button so NVR looks ok

BUT one wire (the grey one) has no continuity from NVR to white terminal block. The brown and black do. So even though the cable looks pristine there must be a break in the grey. The cable is fastened to the frame which is a fold down and fold up all in one u shaped handle and I suspect the frequent folding down (to gain access to grab handles for lifting .. it weighs 50kg ... you cannot lift by the handle there are special grabs) and then folding up to use the plant (or storage) must have weakened the grey wire and its broken.

Will replace the cable tomorrow and update you.

Thanks you ever so much for all your help Lucien. Much appreciated.

Next job is my 240V washing machine motor (which is not running or even offering) So I may well be back on here within the week after I have done some basic tests ...
 
Result! So you had line continuity from the NVR to the motor feed and a return to hold the coil on, but no neutral reaching the motor itself. At least it's a much easier / cheaper repair than something deep inside the motor.

Hopefully the washing machine will yield to similar investigation presently...
 

Reply to 110 V Motor Question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
666
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I picked up a 7.5W 110V TEFC single-phase induction motor for super cheap. I may use it on a home made lathe or stationary-sander for my woodshop...
Replies
7
Views
2K
I am having some trouble with replacing a lighting fixture. I have done many throughout the house without issue, but this one is perplexing me...
Replies
0
Views
517

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock