I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel.

The assembly is a single phase 110v brick hoisting motor and so needs wiring to allow reversing.

There is nothing to work back from as it was all disconnected but I have since gone back to this little project to see if I can get it sorted.

So the motor itself has 3 windings u1-u1, v1-v2 and z1-z2, before I continue I should say this motor is sealed with no access to terminals

u1-u2 and v1-v2 each measure 0.9ohm and z1-z2 measures 1.2ohm, therefore I identify this and the start winding and the other 2 as run windings.

There is a bank of 4 capacitors, 2 pairs wired in parallel, 1 pair being 160uf and the other being 320uf. This is where my confusion first starts because both pairs seem too high to be wired as run capacitors?

The old panel did have a motor starting relay so at least 1 pair of these capacitors does need disconnecting once the motor has ramped up.

There is no centrifugal switch, the motor starting relay serves that function.

So far I know I need to switch z1-z2, to z2-z1 for the reversing feature. I am just unsure as to whether 1 pair of capacitors is to start the motor while the other is always in circuit to offset the single phase supply to one winding considering this motor is essentially a 3 phase motor running on a single phase 110v supply.

The peripheral wiring such as the brake rectifier, limit switches and remote control im fine with, its just the capacitor side and the fact this motor has 3 windings while being in a single phase supply setup.

If anyone can shed any light, I would be very grateful.
 

Reply to Motor wiring help - single phase reversing in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi guys, Been given a motor and associated control gear within a panel that has been water damaged. This motor has 3 windings U1/U2, V1/V2 and...
Replies
2
Views
1K
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
635
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
755
Looking to use this brooks Compton motor as a replacement in an electric cement mixer. can anyone tell me if it is designed to operate off a...
Replies
2
Views
619
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock