Discuss 110V DC Float Earth Ground Fault in the Electrical Engineering Chat area at ElectriciansForums.net

Reaction score
16
Good morning all,

A 'ground fault' alarm came in over the weekend on the 110V charging system. We have two 110V fans currently running and I am suspecting that one is at fault but I can't turn it off yet to fault find. I say I suspect this as we have had to change them before because of low insulation resistance to earth. The motors are on a 3 wire DC system.

The measured voltage to earth on the running motors is
A - Earth 76V
AZ - Earth -44V

The output voltage is currently around 121-123V DC.

Now the strange thing for me is that when i turned on the 110V DC lights that run off the same batteries, the fault clears.

I then measured the voltage again at the motors and got the following

A - Earth -44V
AZ - Earth 76V

I am not 100% clued up on DC floating earth systems. If anyone can help educate me I'd appreciate it.

Ben
 
If its a floating earth then surely the DC voltages cannot be measured to earth, so you will get meaningless results? I may have misunderstood the system though.
 
Floating in the sense that neither wire is solidly earthed, but there is a high impedance connection to earth through the monitoring system. The resistance is low enough that the meter will give a reasonably correct indication of voltage to earth.

It actually sounds like the leakage fault is on the switched line to the lights. With lights switched off, the leakage is pulling the midpoint towards one pole via the lights, when switched on it is pulled an equal amount to the other pole via the switch, hence the voltages to earth swap over.
 
Floating in the sense that neither wire is solidly earthed, but there is a high impedance connection to earth through the monitoring system. The resistance is low enough that the meter will give a reasonably correct indication of voltage to earth.

It actually sounds like the leakage fault is on the switched line to the lights. With lights switched off, the leakage is pulling the midpoint towards one pole via the lights, when switched on it is pulled an equal amount to the other pole via the switch, hence the voltages to earth swap over.

Thanks for this!! I should have realised when turning the lights on that this was the issue. Having so many problems with carbon build up from brushes in the past and other issues I went straight to the motors.

Disconnected one of the 110V lighting circuits and the alarm is completely cleared :thumbsup:
 

Reply to 110V DC Float Earth Ground Fault in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
289
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
780
Hi, I have a project I have been working on, that has me out of my depth with regard to my knowledge, as I am a very basic electronic hobbies...
Replies
5
Views
1K
Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
633

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock