Discuss 110v temporary lighting questions in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

D

dave19

Hi guys, fairly new to industry and even newer to temporary lighting.
We are putting up 5 normal and 3 emergency lights. The lights are being switched via a sensor.
The normal fittings have 3 cores and the emergencies gave 4. The cable from sensor also has 4 cores. How should I connect the cable from sensor to each fitting (both normal and emergencies) ?
 
Could have sworn we had something similar quite recently.
The 4 cores on the sensor are probably live in, switched live out, neutral and earth.
The em lights need a permanent live as well as a switched live, so unless you intend running them on a separate circuit, you will need 4 core cable to each fitting.
On the non em lights, you just connector block the permanent live, with the other 3 cores going to their respective terminals in the fittings.
 
@dave19, please can you fill your profile in or give me a PM to your background, this is basic wiring principles to be honest and will be shown in the information supplied with the PIR and EM lights, are you a practicing qualified Electrician or a trainee, if the latter then you may find applying for access to the trainee section to your benefit, we have mentors and staff who will be very helpful to this level of question.

I'm closing the thread until I receive further information, if your not an Electrician then we are not here to give a step by step guide to doing such work.
 
Last edited:

Reply to 110v temporary lighting questions in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
643
Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
726
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
473
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
490

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock